PLC 32 pt modules

1 REPLY 1
Reply
Message 1 of 2
Anonymous
249 Views, 1 Reply

PLC 32 pt modules

I am building standalone 32 pt plc modules. They are set up with 16 pts on the left ladder and 16pts on the right. They insert fine individually but not with the spread sheet. The first module comes in fine and its addressing is fine. However, subsequent symbols and rung comments for the right side come in on top of the left side. In addition, if multiple modules are in the spread sheet, the 2nd module will not start a new page but comes in on top of the right side of the previous module.
1 REPLY 1
Message 2 of 2
Anonymous
in reply to: Anonymous

John,
Make sure that your Parametric module file contains only 16 Address line type attributes.