When you inserted the block, did you specify the correct sumbol for the additional poles?
It sounds like you used the same symbol for all four poles which would create this sort error.
Thee command should read wd_3 unit VCB11THI VCB21THI VCB21THI VCB21THI based on your attached screen shot.
The fourth character in the symbol name is the identification for a parent symbol or a child symbol.
If you use the parent symbol for all four poles, ACADE will see four different breakers.
A PARENT symbol is the one that normally has all the catalog data and a list of other componentns that ACADE ties to it.
The CHILD symbol normally has the part identification and a link back to to the parent symbol.
To fix your dwg, use the SWAP/UPDATE command and select the appropriate symbol from the 'Circuit Breaker 2nd+ Poles' sub menu in Circuit Breakers and then select each of the additional poles. Acknowledge the warning and proceed for all three.
Next, you need to edit each child symbol, click on 'Parent/Sibling' and select the first pole as the parent for the breaker.
Finally, do a project update and then you should find that ACADE is only reporting the one 4 pole CB in that dwg.
Regards Brad
Brad Coleman, Electrical Draftsman
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
When you inserted the block, did you specify the correct sumbol for the additional poles?
It sounds like you used the same symbol for all four poles which would create this sort error.
Thee command should read wd_3 unit VCB11THI VCB21THI VCB21THI VCB21THI based on your attached screen shot.
The fourth character in the symbol name is the identification for a parent symbol or a child symbol.
If you use the parent symbol for all four poles, ACADE will see four different breakers.
A PARENT symbol is the one that normally has all the catalog data and a list of other componentns that ACADE ties to it.
The CHILD symbol normally has the part identification and a link back to to the parent symbol.
To fix your dwg, use the SWAP/UPDATE command and select the appropriate symbol from the 'Circuit Breaker 2nd+ Poles' sub menu in Circuit Breakers and then select each of the additional poles. Acknowledge the warning and proceed for all three.
Next, you need to edit each child symbol, click on 'Parent/Sibling' and select the first pole as the parent for the breaker.
Finally, do a project update and then you should find that ACADE is only reporting the one 4 pole CB in that dwg.
Regards Brad
Brad Coleman, Electrical Draftsman
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
thank you but you give me a lessons with only word , so it very difficult to me to understand how i can do the right procedure, can you give me a screenshot series that explane the procedure?
i need only one symbol for the four poles, like normal 3 poles CB that there are in IEC ACE library , they have one symbol for 3 poles
thank you but you give me a lessons with only word , so it very difficult to me to understand how i can do the right procedure, can you give me a screenshot series that explane the procedure?
i need only one symbol for the four poles, like normal 3 poles CB that there are in IEC ACE library , they have one symbol for 3 poles
The multi-pole symbols in AutoCAD Electrical are designed to adapt to almost any wire spacing. Brad has given you the correct method for adding a 4-pole symbol to the menu that will adapt to varying wire spacing. If you want a symbol that already has all poles included, at a fixed spacing, you can create this using Symbol Builder. Be sure to select the correct category for the new symbol, like CB, DS, etc., so you get the proper attribute template.
Hint: With a fixed all-inclusive symbol there will be no need for a child symbol. The new symbol will be added to the menu as a normal symbol. You won't use the command trigger method and the wd_3unit trigger.
Doug McAlexander
Design Engineer/Consultant/Instructor/Mentor
Specializing in AutoCAD Electrical Implementation Support
Phone: (770) 841-8009
www.linkedin.com/in/doug-mcalexander-1a77623
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
The multi-pole symbols in AutoCAD Electrical are designed to adapt to almost any wire spacing. Brad has given you the correct method for adding a 4-pole symbol to the menu that will adapt to varying wire spacing. If you want a symbol that already has all poles included, at a fixed spacing, you can create this using Symbol Builder. Be sure to select the correct category for the new symbol, like CB, DS, etc., so you get the proper attribute template.
Hint: With a fixed all-inclusive symbol there will be no need for a child symbol. The new symbol will be added to the menu as a normal symbol. You won't use the command trigger method and the wd_3unit trigger.
Doug McAlexander
Design Engineer/Consultant/Instructor/Mentor
Specializing in AutoCAD Electrical Implementation Support
Phone: (770) 841-8009
www.linkedin.com/in/doug-mcalexander-1a77623
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
All screen shots are utilising the IEC menu so don't worry if the symbols look different.
First screen shot shows the single pole CB entries in the component selection
This shot shows the 2nd pole menu which allows you to add additional poles and auxilliary contacts.
The different attributes between parent (Left) and child (Right) blocks.
Finally, the command I have set up in my Icon Menu to insert a 4 pole CB. IF you type this in, you should get the 4 pole breaker you desire or you can add it to your Icon Menu.
You will notice that I have not bothered to change the icon image from the 3 pole image however the command will insert the 4 pole breaker with no problems.
I added a 4 Pole CB sub menu to the main CB directory which has all the three pole breakers copied and edited to insert a 4 pole CB.
Regards Brad
Brad Coleman, Electrical Draftsman
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
All screen shots are utilising the IEC menu so don't worry if the symbols look different.
First screen shot shows the single pole CB entries in the component selection
This shot shows the 2nd pole menu which allows you to add additional poles and auxilliary contacts.
The different attributes between parent (Left) and child (Right) blocks.
Finally, the command I have set up in my Icon Menu to insert a 4 pole CB. IF you type this in, you should get the 4 pole breaker you desire or you can add it to your Icon Menu.
You will notice that I have not bothered to change the icon image from the 3 pole image however the command will insert the 4 pole breaker with no problems.
I added a 4 Pole CB sub menu to the main CB directory which has all the three pole breakers copied and edited to insert a 4 pole CB.
Regards Brad
Brad Coleman, Electrical Draftsman
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
thank you so much, now I understand,
I had already created (with a procedure similar to yours) a personal 4-poles CB library but I made this error: "wd3_unit VCB11Q9 VCB11Q9 VCB11Q9 VCB11Q9 ", my error is that i write 4 equal VC113Q9
thank you so much, now I understand,
I had already created (with a procedure similar to yours) a personal 4-poles CB library but I made this error: "wd3_unit VCB11Q9 VCB11Q9 VCB11Q9 VCB11Q9 ", my error is that i write 4 equal VC113Q9
I discovered this:
Primary/father pole name VCB1xQx
Second/son pole name VCB2xQx
At the father name it is necessary to change only the fourth numbere from 1 to 2
I discovered this:
Primary/father pole name VCB1xQx
Second/son pole name VCB2xQx
At the father name it is necessary to change only the fourth numbere from 1 to 2
Glad you got it sorted...
Regards Brad
Brad Coleman, Electrical Draftsman
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
Glad you got it sorted...
Regards Brad
Brad Coleman, Electrical Draftsman
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
You can always add additional poles to a 3-pole device using 2nd+ child symbols. That has always been available. Join the child to the 3-pole symbol with a dashed link line.
Doug McAlexander
Design Engineer/Consultant/Instructor/Mentor
Specializing in AutoCAD Electrical Implementation Support
Phone: (770) 841-8009
www.linkedin.com/in/doug-mcalexander-1a77623
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
You can always add additional poles to a 3-pole device using 2nd+ child symbols. That has always been available. Join the child to the 3-pole symbol with a dashed link line.
Doug McAlexander
Design Engineer/Consultant/Instructor/Mentor
Specializing in AutoCAD Electrical Implementation Support
Phone: (770) 841-8009
www.linkedin.com/in/doug-mcalexander-1a77623
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
I agree. I've taught that method for many years. But I don't want other readers to think that the software was designed without an option for handling 4-pole devices. You can add as many poles as needed using 2nd+ method.
Doug McAlexander
Design Engineer/Consultant/Instructor/Mentor
Specializing in AutoCAD Electrical Implementation Support
Phone: (770) 841-8009
www.linkedin.com/in/doug-mcalexander-1a77623
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
I agree. I've taught that method for many years. But I don't want other readers to think that the software was designed without an option for handling 4-pole devices. You can add as many poles as needed using 2nd+ method.
Doug McAlexander
Design Engineer/Consultant/Instructor/Mentor
Specializing in AutoCAD Electrical Implementation Support
Phone: (770) 841-8009
www.linkedin.com/in/doug-mcalexander-1a77623
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
Can't find what you're looking for? Ask the community or share your knowledge.