I have created a custom symbol representing IO connections on a VFD drive. I have nine wire connection points on the symbol and I need to add separate destination arrows for each terminal where the source will be from a PLC output card. I can insert the first destination arrow just fine but when I go to add the next one on a different wire the information for the first one I added is prepopulated and if I change it, it will change it for the first destination arrow and will not add the second. It almost looks like it is behaving like the connections are inter connected in the symbol. Any thoughts? I have attached the symbol DWG file from the library.
Thanks in advance
Solved! Go to Solution.
Solved by rhesusminus. Go to Solution.
I'm not able to replicate your problem, but see some issues.
Your attributes looks fine (what did you bet @jseefdrumr 😉 ), but the block name is a little bit off.
I'm guessing that you want to separate the terminals of ATV320 to a separate symbol?
The block name should not start with VT10. HT and VT are reserved for actual terminals.
Try VDV2 instead, as it's a child symbol.
That being said... When I use your symbol, I've got no problems insert multiple destination signals:
What is your wire trap distance?
Looks like the naming was the issue, I changed the names as you suggested to VDV2* and it works fine. Thanks for the help.