The problem is caused due to you ROTATING the block...
As has been stated, ACADE has two different versions of each block. Each version of the block is set up so that the wires come in from the correct direction. Wire connection direction is set via attribute names for each direction.
When you manually rotate the block, these names are not changed so ACADE tries it's best to connect to the block according to it's programming.
To fix the problem, you need to remove the wires and then the block itself. Redraw the wires in the correct location and THEN insert the block (without rotating it) on the wire. ACADE will insert the correct block according to the wire direction which, as you have noted, works properly.
If you then select the block and check it's properties for the file name and compare that to one of the other relay blocks you will see that they are different file names. The difference being the 'H' or 'V' at the front of the file name.
Now for the bonus information. The Insert Component menu has a tick box in the bottom left corner which selects the opposite orientation of the block you want to insert from the dwg standard. That standard is set by the Ladder Default on the Drawing Format tab in the Drawing Properties. If the Ladder default is Horizontal (like yours probably is) then the tick box is labelled 'Vertical' however if the setting is vertical, then the box is labelled 'Horizontal'.
Be Aware that this check box is carried forward to the next insertion in the session. This means that if you set it for one block, you need to remove the set for the next block unless you want it to be inserted in the different orientation as well.
Regards Brad
>