You're welcome and Happy New Year!
The M1 in the control circuit is the coil, I forgot to label A1 and A2.


Control components are typically drawn separately from power components because the control circuit operates at a much lower voltage than the power circuit. This separation helps improve clarity and ensures safety.
The most common control voltage is Class 2, 24VDC, which is both safe to touch and ideal for operating devices like pushbuttons and pilot lights.
In a control circuit, components such as the coil (A1, A2) and auxiliary contact (13, 14) operate at this low voltage and are specifically designed to control the higher-voltage power circuit indirectly.
On the other hand, the power circuit handles the voltage and current required to drive equipment like motors. The power contacts (1-2, 3-4, 5-6) are responsible for switching this higher voltage like 480V - 600V directly to the motor or other devices. These are drawn on the power side of the schematic for clarity.
Although there is nothing stopping you to draw all the devices together. In your case, The control voltage for the Finder contactor 22.44.0.230.4310 is 230 volts anyway.
1. You can use the 2nd Starter Contact to add aux contacts on power side.

2. Drop a new contact under the power contacts

3. Link the new child contact to the parent coil like M2.




4. Use AELINK command to add a dashed line if you like.


You can also move the coil under if you want to show everything in the same spot.

Arshdeep Singh
C.Tech, CMSE®
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.