Robot Structural Analysis Forum
Welcome to Autodesk’s Robot Structural Analysis Forums. Share your knowledge, ask questions, and explore popular Robot Structural Analysis topics.
cancel
Showing results for 
Show  only  | Search instead for 
Did you mean: 
Reply
Message 1 of 9
Anonymous
919 Views, 8 Replies

P-Delta

Hello,

 

I am a new user of Robot and maybe this is a stupid question but I hope you will be kind enough to reply.

I am performing a seismic LSA on an existing building and I need to include P-Delta effects.

Would it be enough to include the P-Delta on the Load Cases? will that affect the combinations I create from the load cases? Or should I define the P-Delta non-linearity directly to the load combination?

 

When I do the latter, the combination including the seismic load case from the Linear Static analysis does not converge and crashes with Error 5000.

 

Thank you in advance and I would really appreciate your help with this!

8 REPLIES 8
Message 2 of 9
Rafacascudo
in reply to: Anonymous

you have to create it directly for the combinations.

Search the forum for error 5000

Rafael Medeiros
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

Message 3 of 9
mustafahesenow
in reply to: Anonymous

Hi @Anonymous

Send us the model please.



Mustafa Hesenow
Senior Structural Design Engineer/MZP
LinkedIn

Message 4 of 9
Anonymous
in reply to: mustafahesenow

Hi @mustafahesenow

 

please see the model attached

Message 5 of 9
Anonymous
in reply to: Anonymous

Could someone please explain why it does not converge when P-Delta is considered in the seismic combination? It seems to be working fine for the vertical load combinations.

 

Thank you again!

Message 6 of 9
Artur.Kosakowski
in reply to: Anonymous

Hi @Anonymous

 

This is the deformation for linear static analysis.

 

linear static 301.PNG

 

It cannot be that big (as it would be even larger for the 2nd order analysis and this is why IMHO the nonlinear analysts diverges). I'd say that either the seismic loads are too big or the model is wrong (lack of horizontal restrains / diaphragms).

 

If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.

 

 



Artur Kosakowski
Message 7 of 9
Anonymous
in reply to: Artur.Kosakowski

Hi @Artur.Kosakowski

 

Thank you for your reply. I am certain about the seismic loads because I have checked it and compared with the load derived from hand calculations.

As for the model, as already mentioned it is an existing structure relying solely on moment frames to resist the seismic forces. The extensive bracing of the roof should allow it to perform as a semi-rigid diaphragm and similarly the concrete slab for the mezzanine level.

The purpose of the this analysis is to evaluate the building and therefore I would appreciate any assistance I can get for the assumptions already made or those that I might have missed by creating the model.

 

Thank you again for your help so far.

Message 8 of 9
mustafahesenow
in reply to: Anonymous

1



Mustafa Hesenow
Senior Structural Design Engineer/MZP
LinkedIn

Message 9 of 9
Anonymous
in reply to: mustafahesenow

Hi @mustafahesenow

 

Thank you for your reply.

The code parameters you specify are correct when it is regarding new buildings where ASCE 7-10 applies.

For evaluation of existing buildings ASCE 41 is to be followed which specifies much larger forces to reach the real inelastic displacement.

 

Because Robot does not have in-built ASCE 41 parameters, I had to adjust the parameters specified on ASCE 7 to reach the load applied according to ASCE 41 (which really is 81% of total load).

Can't find what you're looking for? Ask the community or share your knowledge.

Post to forums  

Technology Administrators


Autodesk Design & Make Report