Custom PLC Child Component - Unable to Recognize Wire Numbers from Child Component

4 REPLIES 4
SOLVED
Reply
Message 1 of 5
mgaudyK243P
158 Views, 4 Replies

Custom PLC Child Component - Unable to Recognize Wire Numbers from Child Component

My goal is to have a child component behave similar to a PLC I/O component. 

 

I am sure many of you know that the PLC I/O Module can automatically populate the wire numbers going into the I/O module with %F%S%N and "search for PLC I/O address on insert" checked under drawing properties.

mgaudyK243P_0-1679059302577.png

 

I am hoping to make a child component behave the same way.  Unfortunately the wire numbering behavior is different.  I suspect this to be due to some kind of missing tag or link.  In this case I used F%FF S%SS N%NN to show the breakdown of how ACADE is reading this.  Has anybody encountered this before?  Is there a solution?

mgaudyK243P_1-1679059558034.png

 

I attached the parent and child component I am using in case someone wants to test out my setup.

 

I appreciate the feedback.

 

4 REPLIES 4
Message 2 of 5
rhesusminus
in reply to: mgaudyK243P

The block names are completely off. They should start with PLCIO.


Trond Hasse Lie
AutoCAD Electrical and EPLAN expert
Ctrl Alt El
Please select "Accept Solution" if this post answers your question. 'Likes' won't hurt either. 😉
Message 3 of 5
mgaudyK243P
in reply to: mgaudyK243P

That fixed it, much appreciated!

Message 4 of 5
mgaudyK243P
in reply to: mgaudyK243P

The only issue is that it loses the link to be a child component.  

Message 5 of 5
rhesusminus
in reply to: mgaudyK243P

The child TAG-attribute must be "TAG2", not "TAG1". That might be the problem (Haven't looked at the files yet)


Trond Hasse Lie
AutoCAD Electrical and EPLAN expert
Ctrl Alt El
Please select "Accept Solution" if this post answers your question. 'Likes' won't hurt either. 😉