WSNO=>173307
[<EASEMENT>]
#NotSet#
[<PAD MOUNT>]
CONTRACTOR
TO EXCAVATE 8' X 10' X 4' LEVEL BOTTOM PIT
INSTALL 4'-8" X 7' X 4' CONCRETE VAULT TRANSFORMER FOUNDATION AND GROUND MAT
INSTALL 4'-8" X 7' CONCRETE VAULT COVER
INSTALL
225 KVA - 3 PH - 7.2/12.5KV - 120/208V STAINLESS STEEL
PAD MOUNT TRANSFORMER [SP7518].
LABEL TRANSFORMER LOCATION NO. 2780
[<PRIMARY UG>]
#NotSet#
[<SERVICE>]
INSTALL 4 INCH PVC SCHEDULE 40 CONDUIT [SP7316] FROM
LOCATION NO. #### TO LOCATION NO. ####.
IN 24 IN. DEEP TRENCH DUG AND BACKFILLED BY CUSTOMER
INSTALL 180 FT.
350-4/0-350 AL TRIPLEX & (1) 350 KCM AL UG SERVICE CABLES.
TAG CABLES '80-A-84', 80-B-84', '80-C-84' AND
'80-N-84' ON BOTH ENDS.
LEAVE UG CABLE WARNING TAPE FOR CUSTOMER TO INSTALL WHEN BACKFILLING
[<TAKE-OFF POLE>]
INSTALL THREE PHASE [7.2/12] KV L-G OH TO UG
TRANSITION [SP7220].
INSTALL POLE GROUND [SP3800].
INSTALL THREE 27 KV CUTOUTS AND BRACKET FOR UNDERGROUND
[SP3579].
FUSE 25 AMPS
INSTALL 4" PVC PRIMARY RISER & STANDOFFS [SP7328].
IN 36 IN. DEEP TRENCH DUG AND BACKFILLED BY CUSTOMER
INSTALL 231 FT.
OF 3 RUNS
NO. 2 15KV UG PRIMARY CABLES
LEAVE UG CABLE WARNING TAPE FOR CUSTOMER TO INSTALL WHEN BACKFILLING
INSTALL 4 INCH PVC SCHEDULE 40 CONDUIT [SP7316] FROM
LOCATION NO. #### TO LOCATION NO. ####.