Hi Salman,
The reason you are getting this error message is that the Wood Armer equations are really only applicable to moment field of an isotropic flat slab and the program is expecting that the reinforcement set definition is applied to all elements or grillage beams in that sub-model representing the flat slab only.
I have had a look at your model and it appears that sub-model A not only contains the flat slab element but the diaphragm beams and upstand beams also. To get the reinforcement moments for the flat slab only you will need to move the diaphragm and upstand beams into an additional new separate sub-model (in the same plane). This can be done by creating a new 2D sub model (Z=0) and then in the sum model Members form in sub-model A select all the beam members in the table and use the task "Move to sub model" to select the new sub-model.
You will probably be asked about the beam eccentricities being applied which you should answer yes. The model can be checked with the 3D Element viewer to ensure consistency.
If a reinforcement set is then defined just for sub model A this will apply only to the FE deck slab and the reinforcement moments should then be accessible.
It should be noted that as this model is for a composite steel beam deck the reinforcement determined from the reinforcement moments is for slab bending and twisting alone and does include any longitudinal membrane reinforcement required by the composite action of the composite moments. This will be established from the composite beam design checks.
I hope this helps and if it answers your query please mark this post as a solution so that others may benefit. Thanks
Kind regards
Dave Geeves