Robot Structural Analysis Forum
Welcome to Autodesk’s Robot Structural Analysis Forums. Share your knowledge, ask questions, and explore popular Robot Structural Analysis topics.
Thermal Load
27 REPLIES 27
Message 1 of 28
12364 Views, 27 Replies
Thermal Load
I am trying to apply an 80 degree thermal load to the upper surface of an RC Shell but it won't let me specify a temperature in the "surface > thermal loads" window. I can assign a gradient and apply it to the shell but no temperature.
27 REPLIES 27
Message 2 of 28
Rafal.Gaweda
Message 3 of 28
Sorry for the late reply, I've tried these already... I'm designing a flat RC slab and the option to input a temperature is not available.
I do "load definition", trying both "live" and "temperature" but within both of these the program does not allow me to input a temperature, only a gradient as seen in the image attached.
I wish to apply a temperature of 80 degrees C to the top surface of the slab, I'm designing it within "Plate Design".
Message 4 of 28
Rafal.Gaweda
 temperature gradient along an element's thickness , along local Z.
Convention:
gradient value -> on top = +half of gradient value , on bottom  = -half of gradient value.
Rafal Gaweda
Message 5 of 28
in reply to: Rafal.Gaweda
So for a slab thickness 650mm where it is desired to have 80 degrees at the upper surface and 20 at the base.... I would specify a gradient of -60/0.65 = -92.31 oC/m and this will simulate the desired affect?
Message 6 of 28
Rafal.Gaweda
No,
In such case you have to change structure type on Shell then:
if you consider assembling temperature as 0 deg then:
if you consider assembling temperature as 20 deg then (elements have already temp 20 deg):
Rafal Gaweda
Message 7 of 28
Rafal.Gaweda
Important : message 6 updated \ corrected!
Rafal Gaweda
Message 8 of 28
Thanks a lot for the help!
My slab is 650mm deep does this affect the gradient in any way?
Message 9 of 28
Rafal.Gaweda
No ;  gradient between top and bottom layers whatever slab thicness is.
Rafal Gaweda
Message 10 of 28
Refaat
Dear Rafal
What is the meaning of  "assembling temperature" and what is the difference between assembling temperature and  the value of  "dT1" in the "thermal load 3p window" ?
Refaat
Message 11 of 28
Rafal.Gaweda
in reply to: Refaat
This is written just above second screen shot in message 6:
"if you consider assembling temperature as 20 deg then (elements have already temp 20 deg):" - it means starting temp is already 20 so you need to "heat it' +30 and gradient 60.
Rafal Gaweda
Message 12 of 28
Refaat
in reply to: Refaat
Dear Rafal
What about  this situation , how can I calculate the  " temperature and gradient values" in the thermal  load window definition ?
Initial  temp. = 20 c
(Maximum temperature )Summer temp. = + 45 c
(Minimum temperature )Winter temp. = - 5 c
Minimum thermal gradient ,ΔT= (-5-20) = -25 c
Maximum thermal gradient ,ΔT=(45-20) = + 25 c
Thanks in advance
Refaat
Message 13 of 28
Rafal.Gaweda
in reply to: Refaat
The meaning of "gradient" in robot temp panel load is the temp difference between top and bottom layers of panel (difference along panel thickness)
so in your case(s) (I understood the whole panel has the temp +45 or -5 along thickness)
1. Summer : load window setings : Temperature = +25, Gradient = 0.
1. Winter :  load window setings : Temperature = -25, Gradient = 0.
Rafal Gaweda
Message 14 of 28
Refaat
Dear Rafal
Thanks a lot for your advise
Refaat
Message 15 of 28
how should i apply a thermal load with gradiient
external temperature in winter = -15 c
in summer = 40c
internal tempreature = 20 C
i have concrete wall of 20 cm thickness with internal insolation
kindly show me how to calculate the DT and the gradient to use in a Robot model
Message 16 of 28
Rafal.Gaweda
considering initial temp = 0:
summer: Temperature = 30, Gradient = 20
winter: Temperature = 2,5, Gradient = -35
Rafal Gaweda
Message 17 of 28
can u plz send how u calculated the temperature ?
Message 18 of 28
Rafal.Gaweda
Message 19 of 28
If i undserstand your post :
I have only one case of temperature (dT1) for summer and winter : 50 if assembling temperature is 0° C and 30 if assembling temperature is 20° C.
Can you explain how you have 50° C ??
And there is a mistake in your post if i consedering 20° C assembling temperature
30 + 30  = 60 (not 80° C)
30-30 = 0 (not 20° C)
So we have gradient = 60 - 0 = 60.
Message 20 of 28
Rafal.Gaweda
I assume you are refering to second screen shot in post 6
Assembling temperature is the temparature which "already has the panel" so to reach 80 deg on outer fibers you need to add uniform temp of 30 + gradient 60 (which will give 30 on top fibers) so finally on top:  20(assembling ; see text above 80 on screen shot) + 30 uniform + 30 (coming from gradient) gives 80
similar way on bottom
Rafal Gaweda
