Hi,

added main reonforcement 16 s200 and additional reinforcement +1 to edges but additional reinforcement is not counted in calculartions. 1398 mm2 should be covered with main+additional reinforcement.

 

What can cause the problem?

JPNR87_1-1738067384264.png

 

 

JPNR87_2-1738067408761.pngJPNR87_3-1738067427177.png

 

 

Thanks!

 

 

 

 

 

 

0 Likes
158 Views
2 Replies
Replies (2)
Message 2 of 3

JPNR87
Collaborator
Collaborator

Is it possible,that plate with "parameters of foundation elasticity" modeled and calculated in "Building Design " mode is causing this?

 

JPNR87_0-1738070017859.png

 

0 Likes
Message 3 of 3

Simau
Mentor
Mentor

Hi @JPNR87 

Nothing wrong in results

Simau_0-1738070114378.jpeg

 

Main zone T16/200               =  10.05 cm²

Additionnal reinf T10/200   =  3.92 cm²

Total                                         =  13.97 cm²

 

M. Agayr