Hi all
Please find the attached file.
I calculated Vu & phiVc for column 31 manually (using ACI code)
d=167.5mm
density of concrete= 23.6kN/m^3
column dimension: 400x400
service DL=2kN/m^2
service LL=3.5kN/m^2
b1=400+167.5=567.5mm
23.6(0.2)=4.7kN/m^2
1.2(4.7+2)+1.6(3.5)=13.64kN/m^2
13.64[(7.1)^2-(0.5675)^2]=683.2kN
Bo=4(567.5)=2270mm
phiVc=0.75(0.33)sqrt(24)(2270)(167.5)(10^-3)=461.12kN
Using ARSA:
From Forces table:
Fx=652.81kN
From Slabs- punching for panel 17:
Qadm=467.67kN (manually 461.12kN)
Q=268.17kN
467.67+268.17=735.84kN (manually 683.2kN)
It seems as there's a discrepancy in Q value, if I'm understanding it correctly.