Hi @pncad250
- when i go to the Slab Reinforcement Screen the 3d image only shows the upper mat of reinforcing in the 12" slab I can't get it to show the lower mat, I have tried toggling the + and - in the upper left hand corner. What can I do to get it to show lower mat of reinforcing as well?
This should switch between the top and bottom reinforcement. If it doesn't try to use these commands:
Reinforcement > Top
Reinforcement > Bottom

- I am having a hard time interpreting the provided reinforcement screen, the individual square indicates for example, 0.26in^2/ft and the #5x8.27 does the 8.27 imply 8.27" o.c., this seems to contradict the 0.26in^2/ft. or is this a bar length?
0.26in^2/ft is the required area of reinforcement (so 0 corresponds to the part of slab where it is not needed at all unless you want to provide the minimal one). #5x8.27 is what is proposed for the reinforcement bar diameter you set in the reinforcement type assigned to this panel. This can actually be the value of the minimal reinforcement.
If one or more of these posts answered your question, please click Accept as Solution on the posts that helped you so others in the community can find them easily.

Artur Kosakowski