Eurocode 7 - Partial Factors
I'm trying to design a pad footing( 6.0x6.0x2.0m) according to EC7 - DA2.
The imposed loads are
DEAD LOADS:
600ΚΝ vertical load plus self weight of foundation automatically calculated by Robot(6.00x6.00x2.00x24.53=1766.16KN)
LIVE LOADS:
300KN horizontal load
3000kNm moment at the the top of footing.
The design combination for soil capacity is 1.00DL+1.50LL
In the calculation note it seems that the total vertical dead load is calculated with a partial factor 1.00 for the imposed dead load and with 1.35 for the self weight: Ν=1.35x1766.16+1.00x600=2984.32KN.
Is this calculation correct?
Also I would like to ask if it's possible to design according to DA2* (maybe by editting some. rgl file?)
Thank you.
Artur.Kosakowski
Autodesk Support
Autodesk Support
I think it is correct. As both combinations are used for verification. The live load "generates" eccentricity and large eccentricity is unfavourable. The 1.35 factor actually stabilizes the situation despite generation larger stress in soil.
For DA2 - is this what you need?
Artur Kosakowski
Hi Artur,
thanks for the reply.
What I don't understand is why in ULS3 and ULS4 the selfweight of the foundation has a partial factor 1.35 and the dead load has one of 1.00.
SELF WEIGHT: 6.00x6.00x2.00x24.53=1766.16KN
N=600.00KN
Ntot=1.35x1766.16+1.00x600.00=2984.32KN
I believe the correct load should have been (for a favourable action of the dead loads)
Ntot=1.00x1766.16+1.00x600.00=2366.16KN
I mean DA2* (with an asterisk) where partial factors are applied all together  γΕ( Ε)<1 /γR(R).
Artur.Kosakowski
Autodesk Support
Autodesk Support
It is assumed that for the certain load types depending on the verification type only maximal or minimal load factor is used. Please check:
http://help.autodesk.com/cloudhelp/2016/ENU/RSAPRO-UsersGuide/files/GUID-69B741C7-D958-4C83-B4C6-E98...
Artur Kosakowski
Thank you.