Hi,
here comes the model edited and updated, you have to check loads and load combination. Some notes:
1) Work first with your model without seismic loads and, when you have finished with the dimensioning add the seismic loads and combination and run the checks. Usually earthquake, specialy in only one story buildings, is not decisive!
2) I managed to adjust the geometry of the model and I created a list of dimensioning groups.....
3) Your model have seriously problems with buckling, I run a buckling analysis for a ULS case and have this multiplier:
| 0,52 |
| 0,62 |
| 0,70 |
| 0,83 |
| 0,84 |
| 0,92 |
| 0,92 |
| 0,96 |
| 1,05 |
| 1,14 |
If you think that the minimum multiplier must be equal to 10.....and you have 0.52????
4) You have to think about the cross section of the column, I would use HE section instead of 2 UPA,
My opinion, your truss height (0.7m) is too small to cover an almost 16 m span? The average ratio between span and height have to be higher then 1/15....
Insert purlins in your model, they are important for truss bucling restraining.
I do for you the best that I can...now is your turn!!
Cheers

PasProStudio