Deflection Problem
Deflection Problem
MUHANNAD.ABU_ABDO
Message 1 of 14
Deflection Problem
MUHANNAD.ABU_ABDO
I faced a problem while designing RC Beam with central span 5 m and two cantilevers at both ends 1.7m. i set all the perfectness and run the analysis after that this message is show up about deflection !!
My thoughts about ACI code ;
the required depth for both end continuous span equal = span/21 so 500/21=23.8 cm
 the required depth for cantilever span equal = span/8  so 170/8=21.5 cm
So, the section depth is 25 cm which is satisfied ACI Deflection Limits !!
So where's the problem ??
Thanks in advance
Muhannad M.Abu Abdo
Structural Design Engineer
Replies (13)
Message 2 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
I'm not ACI expert however the hand calculations you provided disregard both load and amount of reinforcement which seems a bit strange.
Artur Kosakowski
Message 3 of 14
MUHANNAD.ABU_ABDO
it's not strange !! i'm talking about deflection which is ( SLS ) Not (ULS) you can resist the deflection by depth or reinforcement .. i choose the section depth to meet ACI Code limits as in the pic
it's a normal procedure to find section depth ! it's not from my mind ??
as you can see there's no problem with deflection limit ?? so why is that message ??
Muhannad M.Abu Abdo
Message 4 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
My understanding is that the table you inserted gives you the allowable deflection limit and suggested minimal thickness of a slab or a beam. In general the formulas for deflections looks like this
As you can see there are two factors: load and stiffness. If so, when you increase the load you will increase the deflection and unless I'm mistaken this relation is not visible in your hand calculations. The same, when you increase amount of reinforcement you increase stiffness (both due to the fact you will reduce cracks and as E of steel is larger than E of concrete) so you decrease the deflection. I understand that they may be some guidance (for typical loads and reinforcement ratio) that you may use as the initial estimation of beam height to (standard) span length ratio but IMHO you can't tell that it works for any load.
Have you tried to calculate the real value of deflection for e.g. span according to ACI formulas with use of the cracked stiffness of the beam?
Artur Kosakowski
Message 5 of 14
MUHANNAD.ABU_ABDO
Yes you're right .. but i have to take this in my considerations when i'm dealing with special structures ! but it's ordinary building with normal loads and as double check i designed the same beam by using excel sheet and i didn't get any problem ??
Could you check the model plz ?
thanks in advance
Muhannad M.Abu Abdo
Message 6 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
Could you attach this  calculations?
Artur Kosakowski
Message 7 of 14
MUHANNAD.ABU_ABDO
Plz find the attached file
Muhannad M.Abu Abdo
Message 8 of 14
Refaat
Hi
I think the value that should be compared with (RSA value) is (the value of long term deflection) which is considered the effect of cracking and the final amount of reinforcement.
Refaat
Message 9 of 14
MUHANNAD.ABU_ABDO
Thanks for your kind explanations , is it possible to neglect the effect of long term deflection during design ?
Muhannad M.Abu Abdo
Message 10 of 14
Refaat
Hi
Definitely  " No"
Refaat
Message 11 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
If you want to see the value of 'uncracked' deflection then you may  want to check the values obtained for static analysis of the beam model.
Artur Kosakowski
Message 12 of 14
MUHANNAD.ABU_ABDO
thanks for your response .. i know that but my point is " is it possible in beam design to neglect it ? can i do it without Robot take the long term deflection into considerations ?
Muhannad M.Abu Abdo
Message 13 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
As long as you don't mark correction of the deflection by additional reinforcement you can just ignore these errors (assuming you checked the elastic deflections first and you consider this as sufficient enough). You may also increase deflection limits to avoid the errors to be displayed.
Artur Kosakowski
Message 14 of 14
MUHANNAD.ABU_ABDO
Fair enough .. thanks a lot
Muhannad M.Abu Abdo