Apparent bug with AISC 360-16 unbraced lengths - Calculation of Cb
bjur
bjur
Initially when I run this calc, it fails by a substantial margin.  Simple moment frame but my hand calcs show it should pass.  Robot has it failing by a factor of 5.  So I dig in and when I click on the detailed results tab of the beam calcs, it shows the Cb factor = 0.06.  No clue how it got that number.  Per AISC Section F1, Cb should never be less than 1.0.  So in Robot, here's the initial calcs:
So I open up the "Forces" page and get the following:
When you press the "Calculations" button, robot recalculates Cb to the correct value of 1.27.  It also matches my hand calcs:
But I'm stuck because as far as the printed calcs goes, Robot says it fails...by a lot.  Can we get this fixed?
okapawal
Hi @bjur
Can you attach rtd sample file?  (zip it before pasting)
I will report it to the development team for checking.
Waldemar Okapa
Sr Product Owner
bjur
I just attached the file as a zip.  Thanks so much.