I am using Revit 2019 MEP. I am trying to convince my department that it is worth our while to use Revit for piping pressure loss reports, but am having difficulty figuring out how to properly set-up and troubleshoot a closed loop hydronic piping system. I am currently testing a simple system with one pump, and two water source heat pumps (WSHP's). As I have not found a source that concisely lists the steps/workflow for setting up a simple system like this, I am posting here for documentation and to receive feedback.
Some things I have learned along the way:
- Ensure that under MEP Setting, in Mechanical Settings that the checkbox for 'Enable analysis for closed loop hydronic piping networks' is checked. Otherwise your piping system pressure drops will not report.
- Connectors for all mechanical equipment needs to have the flow-in and -out connectors linked to one another.
- If certain pieces of mechanical equipment are 'driving' (setting) the system flow, like the WSHP's for my example, then:
- Pumps should have their connectors' Flow Configuration set to Calculated (I think?).
- Pumps should have their connectors' Loss Method set to Not Defined (I think?).
- Pumps should have their 'Out' connector's System Classification set to Hydronic Supply (I think?).
- Pumps should have their 'In' connector's System Classification set to Hydronic Return (I think?).
- WSHP's should have one of their connectors' Flow Configuration set to Calculated and the other to Preset.
- You will need to manually enter your Water Flow into the Object Property back in the project, found in the Mechanical category of the object's properties.
- WSHP's should have both their connectors' Loss Method set to Specific Loss.
- You will need to enter your Specific Loss (Pressure Drop for piece of Equipment) into the Object Property back in the project, found in the Mechanical category of the object's properties.
- WSHP's should have their 'Out' connector's System Classification set to Hydronic Return (I think?).
- WSHP's should have their 'In' connector's System Classification set to Hydronic Supply (I think?).
- Once all these variable are set, then you are ready to create your piping system(s). For this example you should create one (or two? I do not know) piping systems and generate a layout in order to calculate your piping pressure loss report.
- If you have already creating piping systems before this variables were set, deleted the piping systems associated with the equipment and piping, set the variables and attempt to set the piping systems again, you will run into difficulties.
I apologize in advance if this tutorial/workflow is available already at some other location on this forum, or in another forum, but I was unable to find the information on my own (I welcome any suggestions on resources that is concise and pertains to the same topic!). Anyways, does anyone have any suggestions, recommendations, and or additional information that would correct and/or complete this workflow? Thank you in advance.