VAV Text Parameter won't display in VAV Schedule

VAV Text Parameter won't display in VAV Schedule

jordan_frey
Explorer Explorer
812 Views
7 Replies
Message 1 of 8

VAV Text Parameter won't display in VAV Schedule

jordan_frey
Explorer
Explorer

I am trying to get the text parameter that's inherent to my VAV family to show up when I create a VAV schedule (I would like 'max cfm' values to populate under airflow column), however when I view the field window to apply to get what I want to show, it does not appear in the window. Is there a workaround for this? It should be fairly simple thing to do and will make creating/verifying schedules in CAD more streamlined, but I don't know if it's a shared parameter limitation. 

 

Any ideas? TIA @Kevin.Lawson.PE 

0 Likes
813 Views
7 Replies
  • VAV
Replies (7)
Message 2 of 8

iainsavage
Mentor
Mentor

It is probably a Family parameter which will not appear in schedules.

Create a Shared Parameter and load it into the family file.

Insert a formula for your new shared parameter = Max CFM.

Reload the family into your project.

Use your shared parameter in the schedule. Edit the column header name if you wish

0 Likes
Message 3 of 8

iainsavage
Mentor
Mentor

You can also try this method (its not the way that I've done it before)

https://help.autodesk.com/view/RVT/2022/ENU/?guid=GUID-18575F0E-A0F3-4032-8BAF-205991E3F3A4

 

This explains differences between different parameter types and their behaviour.

https://help.autodesk.com/view/RVT/2022/ENU/?guid=GUID-AEBA08ED-BDF1-4E59-825A-BF9E4A871CF5

0 Likes
Message 4 of 8

HVAC-Novice
Advisor
Advisor

I create a shared parameter to read the actual airflow from the connector. This will be the maximum flow. 

For minimum or a lower heating flow, I use a separate shared parameter I have to enter manually. but at least the max value is automated. 

 

 

Revit Version: R2026.4
Hardware: i9 14900K, 64GB, Nvidia RTX 2000 Ada 16GB
Add-ins: ElumTools; Ripple-HVAC; ElectroBIM; Qbitec
0 Likes
Message 5 of 8

iainsavage
Mentor
Mentor

I think that in these types of families the Max CFM is supposed to indicate the recommended maximum flow through the equipment/terminal to limit noise and pressure loss rather than representing the actual design flow (peak flow for a VAV system?).

0 Likes
Message 6 of 8

jordan_frey
Explorer
Explorer

@iainsavage I was able to create a shared parameter, "Supply Airflow" and load into the project, however, I need this to be a manual entry where I can enter in the design airflow so I can apply different values of cfm depending on the VAV/room being served. I want this to carry over to my Revit schedule so I can see the VAV numbers next to the cfm for each. It appears to be "locked out" as I can't just enter in my cfm as I did before using a text parameter.  

0 Likes
Message 7 of 8

HVAC-Novice
Advisor
Advisor

make it an instance parameter.

 

If you use the actual flow in the ducts, you can automate the max flow and don't have to edit manually. 

Revit Version: R2026.4
Hardware: i9 14900K, 64GB, Nvidia RTX 2000 Ada 16GB
Add-ins: ElumTools; Ripple-HVAC; ElectroBIM; Qbitec
0 Likes
Message 8 of 8

iainsavage
Mentor
Mentor

@jordan_frey wrote:

@iainsavage I was able to create a shared parameter, "Supply Airflow" and load into the project, however, I need this to be a manual entry where I can enter in the design airflow so I can apply different values of cfm depending on the VAV/room being served. I want this to carry over to my Revit schedule so I can see the VAV numbers next to the cfm for each. It appears to be "locked out" as I can't just enter in my cfm as I did before using a text parameter.  


Your screen captures don't make sense. In one capture you have Design Flow as a Type parameter and Supply Flow as an Instance parameter but in the other capture you have Supply Flow as a Type parameter.

Your original question was how to schedule the Max CFM family parameter.

What you now seem to be wanting is to apply design flow rate to the diffuser and VAV, so:-

  1. In the diffuser family create a Shared parameter as an Instance flow parameter.
  2. Assign that parameter to the connector on the diffuser.
  3. The connector should be Preset, Supply, In.
  4. Load into project.
  5. You can assign flow rates to each individual diffuser and these flows will automatically pass into the duct system and totalise through the system.
  6. In the VAV family create an Instance, Shared, flow parameter and assign that to the connector on the room side of the VAV. Make the connector Calculated, Supply, Out.
  7. On the other side of the VAV unit assign the same shared parameter to the connector and make it Preset, Supply, In. This will pass the flow through the VAV unit and you can schedule it.

See attached document and this excerpt from it:

iainsavage_0-1711135647664.png

 

 

0 Likes