Revit Static Pressure Calculation - Cant test supply air system

nfisher
Enthusiast
Enthusiast

Hi All, 

 

Rather new to this, I created a simple system and wanted to see the pressure drop calculation. unfortunately it wont recognize my supply air system and I cannot figure out why. Any help would be appreciated. 

0 Likes
Accepted solutions (1)
2,084 Views
3 Replies
Replies (3)
Message 2 of 4

iainsavage
Mentor
Mentor

the supply connector on the air handling component needs to be set to Calculated rather than Preset. it will read its value from the connected duct which in turn obtains its value from the sum of the air terminal values.

iainsavage_0-1646075865679.png

 

0 Likes
Message 3 of 4

nfisher
Enthusiast
Enthusiast

I really appreciate the time, and I have one further question - I cannot find where I change it from preset to calculated. Could you assist me on this?

0 Likes
Message 4 of 4

iainsavage
Mentor
Mentor
Accepted solution

Select the equipment and click on edit family.

In the family select the suppku connector.

It is originally set as:

iainsavage_0-1646077589773.png

 

 

Change it to Calculated:

iainsavage_1-1646077656974.png

 

Reload into project.