Panel Scheduling - Phase Problems

anthony_iskandar
Advocate
Advocate

I am new in MEP discipline, my TARGET is to make this schedule:

anthony_iskandar_1-1628301526346.png     anthony_iskandar_2-1628301623636.png

the EFB3 Panelboard (3 Poles 4 Wires) is connected to:

EFB3-1 : A mechanical equipment (3 phase)

EFB3-2 : Three jet fans @ 500VA

EFB3-3 : Three jet fans @ 500VA

EFB3-4 : Three jet fans @ 500VA

Note:  I am confused about jet fans phase, but currently is set to 3 phase

And my panel schedule result is like this:

anthony_iskandar_0-1628301244684.png

Is my result alright?

Or I miss something? Why I can't get 1500VA for EFB-2, EFB-3, EFB-4 in each cell, like my TARGET?

Can a 1 phase equipment connected to 3 phase panelboard? I googled it says can, but when I change the jet fans to 1 phase, it says "The family no longer matches the properties for the Circuit. Disconnect the family from the Circuit?"

0 Likes
Accepted solutions (2)
2,303 Views
10 Replies
Replies (10)
Message 2 of 11

ricaun
Advisor
Advisor
Accepted solution

Probably you are setting the wrong voltage or something...

 

By the look, your main system is 120/208 Wye (Check if has 4 Wires on the Electrical Setting).

 

To create 1 phase you need to set your Voltage to 120 V and then connect to the main panel.

 

If you change the family when the circuit is connected Revit probably disconnect by default. Recreate the Power circuit and connect it to the main panel.

 

If you are using Electrical Equipment, after you create a Power circuit you should select a Distribution System of the panel. This should fix some not-found panel problems.

 

See yaa!

Luiz Henrique Cassettari

ricaun.com - Revit API Developer

AppLoader EasyConduit WireInConduit ConduitMaterial CircuitName ElectricalUtils

0 Likes
Message 3 of 11

anthony_iskandar
Advocate
Advocate

Okay, so I changed the exhaust fans phase to 1 phase by also change the exhaust fans voltage to 120V and it worked, and the result is okay, but why the Total Load isn't equal to 8167VA? How to change the Amperes? When I change the 20A to 6.8A or 30.4A, it says "Total connected load for Circuit EFB3-1 is exceeding 80% of the defined rating (7 A)." or "Total connected load for Circuit EFB3-1 is exceeding 80% of the defined rating (30 A)."

Thank you so much before.

Untitled.png

0 Likes
Message 4 of 11

ricaun
Advisor
Advisor

The Rating parameter is used to set the protection of the circuit and control the Wire Size.

 

By the Revit rule, the Rating value needs to be 1.25 times the circuit Current or can not exceed 80% of the Rating value.

 

About the Total Load, looks like your Exhaust Fan circuit has some Demand Factor or something.

 

Check the Load Classification, could be that.

Luiz Henrique Cassettari

ricaun.com - Revit API Developer

AppLoader EasyConduit WireInConduit ConduitMaterial CircuitName ElectricalUtils

0 Likes
Message 5 of 11

anthony_iskandar
Advocate
Advocate
But as you can see in my TARGET table (first post), the Amperes didn't match with mine, is this okay?
0 Likes
Message 6 of 11

ricaun
Advisor
Advisor

I tested and works fine.

 

ricaun_0-1628604302783.png

 

Your first circuit is an Electrical Equipament?

 

Luiz Henrique Cassettari

ricaun.com - Revit API Developer

AppLoader EasyConduit WireInConduit ConduitMaterial CircuitName ElectricalUtils

0 Likes
Message 7 of 11

anthony_iskandar
Advocate
Advocate
You mean you changed the Amperes? How?
Yes, I use "lighting and appliance panelboard", I don't know should I use this kind of panel board, or switchboard, or single phase circuit (but duplicate to 3 phase)?

Please type your reply above this line -##
0 Likes
Message 8 of 11

ricaun
Advisor
Advisor

Here is my sample project (Revit 2021).

 

I change the template panel to Apparent Current. I suppose this is what you want...

ricaun_0-1628605927827.png

 

 

 

Luiz Henrique Cassettari

ricaun.com - Revit API Developer

AppLoader EasyConduit WireInConduit ConduitMaterial CircuitName ElectricalUtils

0 Likes
Message 9 of 11

anthony_iskandar
Advocate
Advocate
Ah, I didn't see your attachment before this, yes actually my first circuit is electrical equipment 3 phase.
I'll try it tomorrow, big thanks!
0 Likes
Message 10 of 11

anthony_iskandar
Advocate
Advocate

Based on this picture, CKT 1 should be the 30.4A electrical equipment (3 phase, R, S, T), then CKT 2, 3, and 4 are the 6.8A exhaust fans with CKT 2 on S, CKT 3 on T, CKT 4 on R. Is it possible to manage these details in Revit?

anthony_iskandar_1-1628301526346.png

0 Likes
Message 11 of 11

ricaun
Advisor
Advisor
Accepted solution

Of course is different... Your diagram voltage is 220/380V.

 

Electric 101:

Power = Voltage x Current.

 

On Diagram you are using 220/380V.

 

CKT 1:
Power: 20000VA
Voltage: 220V
Current = 20000 / 220 / 3 ~= 30.3A

 

On Revit you are using 120/208V.

 

CKT 1:
Power: 20000VA
Voltage: 120V
Current = 20000 / 120 / 3 ~= 50.5A

 

Configure your Revit Voltage right and should work fine!