Panel schedule Connected and estimated current are totally wrong

Panel schedule Connected and estimated current are totally wrong

HVAC-Novice
Mentor Mentor
377 Views
2 Replies
Message 1 of 3

Panel schedule Connected and estimated current are totally wrong

HVAC-Novice
Mentor
Mentor

I use R2026.1 and have this 208V/3 panel schedule and everything looks correct. Except the highlighted " Connected Current" and " Estimated Demand Current". and it is extremely wrong. First row should be 25A, but shows 8A (even if i divide by 1.73 it still doesn't' make sense)

 

HVACNovice_0-1749674001436.png

I saw some threads about some of those things being wrong in old versions. Maybe I just don't understand what the values mean? 

In the template editor They seem to be what they say they are:

HVACNovice_1-1749674267237.png

These are my load calculation settings, and both options yield the same result. 

HVACNovice_2-1749674373896.png

Somewhere i read it may be related to power factors not being 1. But what really is weird, the first few columns (up to " Estimated demand (VA)" seem correct. and i thought the current will be calculated from that?  

 

is this a Revit issue, or am i just not understanding what those two values are? 

 

 

Revit Version: R2026.4.2
Hardware: i9 14900K, 64GB, Nvidia RTX 2000 Ada 16GB
Add-ins: ElumTools; Ripple-HVAC; ElectroBIM; Qbitec
0 Likes
Accepted solutions (1)
378 Views
2 Replies
Replies (2)
Message 2 of 3

russellvee
Advocate
Advocate
Accepted solution

The value for total demand current is averaged across all three phases. You have 25 amps of clothes dryer load on phase B but 0 amps on phase A and C so the average amps per phase is 8.33. It's also 3000VA/208V/sqrt3.

 

Also, clothes dryers will normally be a 2-pole 30 amp circuit and the the NEC has a minimum of 5000 watts each for load calculations. 12.5 amps at 120 volts won't do much drying.

Message 3 of 3

HVAC-Novice
Mentor
Mentor

OK, i think i get it now. Looks like user error 🙂

 

Revit Version: R2026.4.2
Hardware: i9 14900K, 64GB, Nvidia RTX 2000 Ada 16GB
Add-ins: ElumTools; Ripple-HVAC; ElectroBIM; Qbitec
0 Likes