Hello,

 

I get error 'Sizing Failed. Flow for section is 0' when trying to calculate flow (using revit calculation) in a really simple circuit utilising a pump I've made, and I cannot figure out what I've done wrong.

 

Attached is the pump family and a capture of the circuit and error I get.

 

I'm fairly sure it's something to do with the hydronic connectors of the pump, as if I disconnect the pump the sizing works fine. I've tried it with the connectors linked, connectors unlinked, etc etc, but so far to no avail.

 

Any suggestions / pointers?

0 Likes
Reply
471 Views
6 Replies
Replies (6)

iainsavage
Mentor
Mentor

If the 3 units are what generate the flow rates then they should have connectors set as Preset, one would be hydronic supply, the other would be hydronic return. They must be directional, they cannot be bi-directional.

Pump would usually have Global and Bidirectional connections.

0 Likes

iainsavage
Mentor
Mentor

Your return suction connection on your circulating pump also needs to be Calculated, not Preset.

0 Likes

Dominick_ColwillWEQWT
Community Visitor
Community Visitor

Hi Ian, I've realised I posted with the wrong account before. my bad.

 

Thanks for the advice, I've now changed to calculated, reloaded the family and still get the same issue.

0 Likes

iainsavage
Mentor
Mentor

Could you upload your model and I'll take a look at it?

 

0 Likes

craigjonnson
Collaborator
Collaborator

You need to have your connectors linked and both connectors set to system. Martin Schmid at Autodesk did a great write up on Understanding connectors called getting into the flow. Everything you need is explained in there.

Ive attached another post that talks about a similar issue and applying the flow factor.

Microsoft Word - ME204-3 Getting into the.docx (typepad.com)

Solved: Two parallel pumps - Autodesk Community - Revit Products

0 Likes

iainsavage
Mentor
Mentor

There was only one pump in the diagram. Parallel flow considerations shouldn't matter for that simple circuit.

Connectors would normally be Global, Calculated, Bidirectional and I created a small test model to check that it worked.

@FacilityEng2_UK please upload your model if you want more help.