How to eliminate neutral from wire size in panel schedule

shpakkala
Contributor
Contributor

Hi all,

 

I am trying to create a new panel schedule template that shows wire sizes. This I accomplished. The problem is to not have a neutral show in the wire size column for a load in which I do not want a neutral. I created a new type of wire that didn't include the neutral and used that wire, but it still shows up in the wire size column in my panel schedule. I have read multiple forums but can't seem to get any help so far. 

Any help would be greatly appreciated!

0 Likes
Accepted solutions (1)
1,554 Views
5 Replies
Replies (5)
Message 2 of 6

fabiosato
Mentor
Mentor

Hello,

 

In the wire types, in the electrical settings, uncheck the column Neutral required.

Fábio Sato
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

0 Likes
Message 3 of 6

sujanc
Advocate
Advocate

Go to electrical setting>wiring types>neutral required unchecked. 

 

Neutral.jpg

 

Hope this will work.

Please select "Accept solution" if the information was helpful (This allows other users with the same issues to find it higher in search results), or reply back if you need more help!
0 Likes
Message 4 of 6

shpakkala
Contributor
Contributor
That is what I did. I assumed I could just change the wire type to the new type but that is not the case. I had to completely delete everything on the circuit and then put it all back in. After I assigned the devices to a panel I then chose the new wire type and now there is no neutral. So simply changing the type of wire on an existing circuit will not get rid of the neutral.
0 Likes
Message 5 of 6

fabiosato
Mentor
Mentor

Hello,

 

Unfortunally some settings are done only when you create the components or circuits.

Fábio Sato
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

0 Likes
Message 6 of 6

O.Manningham
Participant
Participant
Accepted solution

I know this is an old Topic, but the other thing to change is the electrical connector of the family that is connected to the circuits:

The system type of the connector needs to be: Power - Unbalanced

 

So you need these two things : 

 

Electrical Connector of type : Power - Unbalanced

Wire type that doesnt requires a neutral.

 

Then and only then will the neutral wire be removed from the circuit.

0 Likes