@johnstewart01hvac wrote:
For a multi-zone concealed duct HVAC system, the electrical demand factor reflects that not all zones operate at peak load at the same time. This allows designers to size electrical capacity more efficiently while still supporting simultaneous cooling or heating demands across multiple zones.
For a VRV system, you have most power going to the outdoor unit with the compressors. There you use the electrical data that manufacturer gives you (THEY worry about diversity, or if heating or cooling is larger, the demand is driven by compressor size). As electrical engineer you only need to know; " 208V and 72A", which is on their data sheet. In addition, the single zone units have line voltage to run their fans (and operate the controls, valves etc.). Each of those zone units also will have electrical data (i.e. "120V, 3A"). You don't worry about heating/cooling since the manufacturer will give you the design data. And even under partial load, all fans could be running (for ventilation etc.) at the same time.
The data the manufacturer gives you will work for design and account for startup current etc. You don't need to apply your own logic or theories or ideas how the equipment operates all day long. Yes, in reality it will run at less load most the time. But you also need to size the system in case the system isn't set up properly, starts up, or has some other reason to run parts at 100%. We are not designing for the system to work well 99.99% of the time. We also cover that 0.01%, and that is what the manufacturer supplied design data do.
Don't size the system smaller than the manufacturer tells you just because you think diversity or other conditions require less.
Revit Version: R2026.4
Hardware: i9 14900K, 64GB, Nvidia RTX 2000 Ada 16GB
Add-ins: ElumTools; Ripple-HVAC; ElectroBIM; Qbitec