Hi,
I have a repeated Bathroom core with slight variation in the location of the Plumbing fixtures within that core.
I created a nested family that allows me to move the plumbing fixtures around as needed to fit the architecture's placement of these fixtures.
My question is, can i have these connected with to each other and to a main external connector visible to the hosting revit project? This way even if i move a fixture, it stays connected to its necessary pipes, and i do not have to redo the connectivity of each fixture all over again?
Solved! Go to Solution.
Solved by L.Maas. Go to Solution.
Piping are system families and can thus not be loaded inside a loadable family. Also connectors inside a family only work in the host family and will not be visible when inside a nested family.
Louis
Please mention Revit version, especially when uploading Revit files.
That's a shame... i was hoping that Revit has matured enough to do be able to see within a family.
i guess,. i have to use an Assembly for now and adjust Fixtures according to the room they're in.
Thanks a lot for your response...
Regards,
Fawzi