Air balance schedule "improper use of boolean expressions"

eruesswickG7LDL
Participant
Participant

Im creating an air balance schedule and hitting the wall. Using spaces for schedule. Ive created a field for AIA ACH where I manually input the number of air changes. Trying to use that in a formula to calculate AIA CFM (Volume * AIA ACH/60) and get "improper use of boolean expressions". Did anyone figure out how to do this or a work around? Thank you in advance.

SCHEDULE.jpg

0 Likes
258 Views
5 Replies
Replies (5)
Message 2 of 6

iainsavage
Mentor
Mentor

Although it says its improper use of boolean expressions, I wonder if its actually due to inconsistent units.

Your CFM test will have units of cfm, your volume is cf but your ACH is I assume a unitless number, as is your numerator (60).

So in terms of units you have cfm = cf which is obviously wrong. You would need to include minutes in your numerator to end up with cfm = cfm e.g. Volume*AIA ACH/60 minutes.

 

At least, I think that might be your problem but maybe someone else can help more.

0 Likes
Message 3 of 6

HVAC-Novice
Advisor
Advisor

What are all the units in your equation? Volume should be ft³. And you want to get ft³/minute. 

is "AIA ACH" just a number (unitless)?

 

Revit Version: R2026.2
Hardware: i9 14900K, 64GB, Nvidia RTX 2000 Ada 16GB
Add-ins: ElumTools; Ripple-HVAC; ElectroBIM; Qbitec
0 Likes
Message 4 of 6

eruesswickG7LDL
Participant
Participant

I should have clarified. Im doing hospital design with designated minimum air changes per hour. Yes, the AIA ACH is a unitless number

0 Likes
Message 5 of 6

HVAC-Novice
Advisor
Advisor

@eruesswickG7LDL wrote:

I should have clarified. Im doing hospital design with designated minimum air changes per hour. Yes, the AIA ACH is a unitless number


Divide volume by "1 ft³" and multiply the result by "1 cfm" make sure the numbers are correct (doing the 60-conversion correctly etc. ) . Basically with any equation, manually calculate and see if it works correctly. Especially with made-up unitless numbers. 

Revit Version: R2026.2
Hardware: i9 14900K, 64GB, Nvidia RTX 2000 Ada 16GB
Add-ins: ElumTools; Ripple-HVAC; ElectroBIM; Qbitec
0 Likes
Message 6 of 6

eruesswickG7LDL
Participant
Participant

This worked! Huge thanks.