Agree with Aaron-- we need to provide more specific suggestions. I have some suggestions below....

 

  • Scheduled conduit run lengths are doubled when using the parallel conduit feature as well as the offset feature. Currently the parallel conduits feature is being treated like a parallel feeder and not an independent conduit run.
    • Provide a Boolean toggle in the electrical settings to treat each run as a separate length.
  • Project parameters assigned to conduit/conduit runs/conduit fittings currently do not carry over values.
    • Allow conduit system families to carry over project parameter values. This will allow scheduling to be much more manageable for the end user.
  • Project parameters assigned to conduit runs cannot be scheduled.
    • I am sure most everyone uses the comments parameter because this is the only parameter that will carry over values from a conduit run and is the only parameter that will read correctly on a conduit run schedule. Currently project parameters cannot be used in a conduit run schedule without the assistance of Dynamo. My suggestion is to allow project parameters to be treated identically from a programmatic standpoint as the comments parameter. 

I have more ideas/bug fixes but in my experience these seem to be the biggest pain point for everyone drawing conduit in Revit. Any other ideas on this topic?