Collaborator

It is very important. See example below of an overloaded panelboard that Revit shows as being A-OK. Overall panel demand is 89A, but Phase A demand is 125A. The panel is overloaded and Revit has no clue. It also happens to be unbalanced, but Revit does it's auto-balancing on connected load. That, also, should be done based on demand. I, too, have seen engineers refuse to use Revit's panel schedules because it doesn't do this calculation.

 