This isn't adding the fixture units in a stacked system because of the connector settings; the fixture units leaving the carrier is specified as 8, so it will always be 8.  If you change the carrier to a fitting the fixture units will flow through, but you have to connect a separate family for the water closets.  You will then get the fixture units calculating as you wish, but will have to adjust for the venting.