No; there is a unit within the panel and each device within the unit is connected to the panel, but this is really for circuit number and panel information only. Don't show load info on the panel - turn it off in the Panel Schedule Template. The panel is unconnected (no load info is transferred from it to the overall building system) because it can't do calcs based on 220.84.
Create a separate electrical fixture that does the 220.84 calcs and connect that fixture to your meter center.
I don't have a good working example to share with you right now or I would.
It's not a quick-and-easy thing to set up but it is possible.