P-Trap Orientation

Anonymous

P-Trap Orientation

Anonymous
Not applicable

I am running designlines for waste and vent with sanitary fittings. I have places where I need to put p-traps. Some p-traps come in at the correct orientation. However,most of them I am placing do not.

 

P-Trap Orientation.jpg

0 Likes
Reply
1,125 Views
5 Replies
Replies (5)

rptjr
Enthusiast
Enthusiast

I think that has to do with your source point. Source should be the lowpoint of the sanitary system. On vent I make it the high point.

Where is your source point on the affected p-traps?

0 Likes

greg.mosher
Contributor
Contributor

It not only has to do with the Source Point but the direction of takeoff for the P-Trap. For Desig Line you want the direction in to be from the top of the P-Trap and not the leg. With the attacher arrow it would be reversed with the direction in from the leg. We use the P-Trap with Design Line and the attacher arrow so I have a button script set to "takeoff by other end" set as the default.

GAMosher
0 Likes

bknapton
Enthusiast
Enthusiast

It depends on the design line source along with flow direction.

0 Likes

lei.qiao
Alumni
Alumni

Following two items will impact the direction of the P-Trap.

  • The location of inlet & outlet of the P-Trap. the settings should make the connection indicators the same with 2nd image.

Inlet & Outlet.pngInlet & Outlet_Image.png

  • The setting of the service. It must be set as "Extract" for the drainage service.

service setting.png

When both above settings are correct, the behavior of the P-Trap will be correct. You could check if the P-Trap with incorrect behavior has the incorrect settings.

 

Hope my reply will be helpful.

0 Likes

Anonymous
Not applicable

I too have this same problem and all of the solutions listed on this thread do not fix the issue. Is there anything else that could control this?

0 Likes