Conical Tap Connection

jtorres48H7H
Explorer
Explorer

I have this problem with the conical connections. In the screenshot I have a 12Ø conical and a 12Ø straight as well. I need both connections to be accuflange. Where can I change the conical connection in the database so that it comes out automatically?

 

jtorres48H7H_0-1692418636013.png

 

Reply
Accepted solutions (1)
427 Views
2 Replies
Replies (2)

craigjonnson
Collaborator
Collaborator
Accepted solution

You Can set your C1 & C2 Connectors within your round specifications and leave the connectors on your itms set to none and not locked. Using the specifications you can set your connectors up by size. So if everything over 12" is flanged but below is bead and slip, then this is how you would do it.

jtorres48H7H
Explorer
Explorer

Thank you so much

0 Likes