Hello @Anonymous,
here are the step to follow to apply correctly an external fan BC :
External fan is another way to move flow in or out of a device. An external fan is defined as a head-capacity curve, resulting in an inlet flow rate that varies with the pressure drop of the device. This is a convenient way to determine the operating point of a fan for a particular flow path.
To assign an External Fan condition:
- Set the Type to External Fan, and set the Unit type.
- Enter the rotation speed of the fan in the Rotational Speed field.
- If needed, change the rotational direction by clicking Reverse Direction. The direction is drawn with an arrow.
- Specify the fan curve by clicking the Fan Characteristic Edit button.
- Click Insert to add rows between defined rows.
- Click the Plot button to view the plot.
- The Import button imports a comma separated variable (CSV) file, and the Save button saves the curve information to a CSV file.
- To enter a fan that pulls flow (at an outlet), enter all flow rate and pressure values as negative.
- Enter a slip factor (between 0 and 1) in the Slip Factor field.
- Click Apply.
Note: The slip factor is the ratio of the true rotational speed of the flow to the rotational speed of the fan blades. Due to inefficiencies in the fan, slip can result in a slower flow tangential flow velocity than expected. Autodesk® CFD determines the flow tangential velocity component by multiplying the slip factor by the user-supplied fan rotational speed. The default slip factor is 1.0. This means that the rotational speed of the flow is the same as the rotational speed of the fan.
does it answer to your question ?
If you have other question don't hesitate
Fred