CO Generation in Car park
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report
Hi. I need help on Car park ventilation system . Car park consist of -
1. Two Jet Fan= 1200 l/s
2. Opening (car entry/ exist)= 9 ppm CO concentration is assumed at all-natural ventilation.
4.CO Generation =0.0846 g/s
5. Mechanical exhaust= 5600 l/s
objective :- To find CO concentration and to find optimal location of jet fans .
I have created the model in Revit . It is assumed that CO source are located in Driveways . This is what i have done .
Material,
scalar mixing of Air & CO
Density of Air :- 1.225 kg/m3
Density of CO :- 1.14 kg/m³
Two Jet fan with flow 1.2 m³/s and 1200 rpm
Boundary condition,
At co vent :- Mass flow rate =0.0846 g/s , scalar transient
At Mechanical exhaust :- Volume flow rate = 5600 l/s, scalar transient
At Jet fans :- Volume flow rate = 1200 l/s, scalar transient
At ramp / Natural air inlet = pressure 0 , temperature=26 °C , scalar = 0.000009
Solution,
Transient for time = 1 hrs
Diffusion coefficient of CO in air = 0.662 cm2/s
Problems :-
CO concentration does not change with time and i am not getting proper results. I cannot justify use of jet fans from my result . I ran it for 1 hr and my CO concentration decreased to 2 ppm at end which is not possible so there is something wrong with my boundary conditions . I am new to Autodesk CFD i have used Ansys Previously and my results are completely different . I have attached CFZ file please review the file and let me know fixes i need to make.