Syed needs to read the thread accurately to understand the problem.
1. I chatted with Autodesk yesterday via online chat, trying to explain the simple problem that logging in to my account on Autodesk, and following the prescribed paths of accessing tech support and open cases simply did not work. When I tried to do so, the site told me I didn't have authorization to do so. The individual I was chatting with seemed incapable of understanding this. She opened a case that I couldn't access, then it was cloned to another case, which was closed without solution. I tried contacting Autodesk both through the email as suggested by Autodesk, and also through their website. Neither produced a response. I'm curious...are you the last tech support person available for SimCFD?
2.
a. The 2400cfm is a fixed flow.
b. In typical condenser A/C units, there is in reality leakage around the fan. In the real world, many don't have shrouds, so within the device there will be leakage.
c. In the two design configurations I'm testing, the fan is mounted about 4" off of the outlet port, and the other is with the fan flush to the outlet port. Neither has a shroud in the real application, so this is the environment I must somehow replicate within the analysis. Placing a shroud around the fan will not be real-world conditions.
d. What geometry do I need to create to use the bulk calculator so I can determine what the actuall flow volume is through the curved condenser in both design scenarios?
e. The goal is to understand air volume flow rate so we can understand whether the client is getting sufficient flow through the condenser to perform the phase change of the freon in an ambient temp of 90 degrees F.
f. I've performed multiple analysis while changing the resistances of the material representing the condenser coil. I performed a baseline study to try to determine those resistances. I used the formulas provided on your website to create the resistance values. However, when I use those values, the baseline did not perform equivalent to the manufacturer's specifications. I had to change the resistance value to duplicate what they claimed.
g. When I used those resistance values in a modified geometry of the condenser, the flow through the condenser significantly dropped off, and the pressure drop increased far beyond what the manufacturer claimed for their unit. I thought this was a result of the modified geometry and recirculation, but since I'm being told that might not be accurate, I have no clue what I'm seeing.
h. With reduced recirculation, I'm seeing only 1/6th the flow through the condenser than I am through the fan. That increased to that amount when I used the values I had to use to run the baseline study to determine the resistance values mentioned in step "f".
i. By hand calculations, your formulas for resistance material properties told me to use 0.25 as the resistance. I did, and it did not produce what the manufacturer claimed. I subjectively changed that until I got the proper thermal results of the baseline model...which required a resistance around 0.4~0.5.
The latest study share file, stripped, is 12.4MB. Here's the link to download:
https://www.hightail.com/download/ZWJYNnFPcTIzMWwzZU5Vag