MULTI-PHASE SYMBOL INTERNAL SPACING

Anonymous

MULTI-PHASE SYMBOL INTERNAL SPACING

Anonymous
Not applicable

HOW CAN I MODIFY THE INTERNAL SPACING INSIDE A MULTI-PHASE SYMBOL (i.e. 3 POLE CIRCUIT BREAKER) IN ORDER TO AVOID INTERNAL INTERFERENCE, PLEASE CHECK ATTACHED PHOTO3 pole circuit breaker.png

0 Likes
Reply
Accepted solutions (2)
2,889 Views
5 Replies
Replies (5)

rhesusminus
Mentor
Mentor
Accepted solution
You can do one of two things:

1. Start using 10 mm/units for wire spacing.

2. Change the symbols, so that the are 5 mm/units wide instead of 10.


Trond Hasse Lie
EPLAN Expert and ex-AutoCAD Electrical user.
Ctrl Alt El
Please select "Accept Solution" if this post answers your question. 'Likes' won't hurt either. 😉
0 Likes

rhesusminus
Mentor
Mentor

Well, that being said.. 10 year ago I create a 5 mm/units library for a customer that don't exist any longer, so attached you'll find the files needed!

 

Set up the libraries like this:

2017-06-06_13-50-07.png

 

And then your drawing might look like this:

2017-06-06_13-51-47.png

 

 


Trond Hasse Lie
EPLAN Expert and ex-AutoCAD Electrical user.
Ctrl Alt El
Please select "Accept Solution" if this post answers your question. 'Likes' won't hurt either. 😉

Icemanau
Mentor
Mentor
Accepted solution

The component spacing is set by the wire spacing.

Increase the space between wires in your settings and ACADE will automatically place the components on the wires.

 

Go to the Dwg properties and select the Drawing Format tab.

In the Multi Wire Spacing, set the distance to 10 or higher.

 

To draw a multi wire bus, you select the Multiple Wire Bus tool, set the number of wires and the starting method and click ok to draw. The wires are then drawn at the spacing you have set. NOTE that you can override the setting in the drawing properties when using the Bus tool if you need to.

 

The other option is to edit the blocks themselves and either make the box around the blocks smaller or remove them altogether.

 

Regards Brad

>

Brad Coleman, Electrical Draftsman
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.

EESignature

a01284215
Community Visitor
Community Visitor

I tried placing the folders but my symbols are still 10 mm. I applied settings and everything.

0 Likes

rhesusminus
Mentor
Mentor

You should run the PURGE command to remove the old unused blocks before trying to insert them again.


Trond Hasse Lie
EPLAN Expert and ex-AutoCAD Electrical user.
Ctrl Alt El
Please select "Accept Solution" if this post answers your question. 'Likes' won't hurt either. 😉