Well...it sort of depends on your needs.
Are you duplicating something, like a conveyor line, and are facing the prospect of having several junction boxes, etc with the same names?
Or do you just have a single, sprawled-out system, with a main panel and then some smaller remote ones?
If you're facing the first scenario, you'll probably need to make use of location and installation codes, and if you're following the IEC standards then the issues outlined by CCAD come into play. They're valid issues, so if you're using IEC, you very well could be facing the need for a workaround. But, again depending on your needs, you might be able to slide with location/installation under the NFPA standard. (It doesn't care how you use location and installation codes at all.)
If you're facing the second scenario, it's relatively easy so long as you don't have a ginormous number of remote panels. Where I work, our projects always fall within that second scenario. We always have remote panels, and operator panels/consoles. We manage it all within one project. Our current machine has one main panel and ten remote panels, plus two operator panels and about 30 small junction boxes. That project clocks in at around 120 pages, and sometimes it gets annoying scrolling through the project list to find drawings. But keep in mind, that's an interior and exterior layout for every remote panel and operator console, plus around 85 pages of schematics.
I can't post a whole project here, but in case it helps, I posted a screenshot of the drawing index for the project I mentioned. It shows all the drawings, in the order they appear in the Project Manager.
Hope this helps,

Jim Seefeldt
Electrical Engineering Technician