Good afternoon.
In the project attachment.
On the first, third and fifth sheets, the contact 21, 24 of the relay 1KL1 is repeated.
But when checking the "Check Autocad Electrical" errors are not issued.
Why, and how to make it show error?

 

0 Likes
478 Views
2 Replies
Replies (2)
Message 2 of 3

TRLitsey
Advisor
Advisor

Hi there,

 

Just a thought. have you checked that the tags are correct?  As in are the 1KL1 and not 1KL 1?  Have you run the project rebuild tool before running the report tool?

 

And I would ask, did you use the ACE COPY COMPONENT tool or did you use the AutoCAD COPY / PASTE tool.  Most times ACE will not see a duplicate if you are using AutoCAD COPY / PASTE tool.

 

 

Good luck

 

 

 

Screenshot - 7_11_2017 , 8_16_33 AM.png

Please mark as a solution if this works for you, kudos are always welcome
0 Likes
Message 3 of 3

TRLitsey
Advisor
Advisor

And by the way, when you first insert the coil you can define what the pin list or contact arrangement is.  ACE will keep track of which ones are used and which ones are still free.  You will have to over ride the warning to force a duplication.

 

Good luck

 

 

Screenshot - 7_11_2017 , 2_45_48 PM.png

 

 

 

If it is a relay you use often you can add it to the database with the coil and contact definitions.  You can read up on that using ACE Help tool.

 

 