    <title>topic Re: Conduit OD Not Modeled Correctly in Revit MEP Forum</title>
    <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10234214#M25356</link>
    <description>&lt;P&gt;So OOTB at least for Revit 2020 (I assume for all years) the electrical settings for a 3/4" EMT is the OD is set to 15/16".&lt;/P&gt;&lt;P&gt;When modeled this is actually modeled at 59/64". This is closer to the actual size of the conduit.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;If you go in and edit this OD to something else no surprise Revit rounds to 1/32", but when you actually model the conduit the OD matches what it rounds to.&amp;nbsp;&lt;/P&gt;&lt;P&gt;So you can't get the conduit OD back to 59/64" once you edit the OOTB settings.&amp;nbsp;&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;Again not sure why Autodesk is rounding these settings when the rest of Revit is 1/256" accuracy.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;For the conduit creation you can edit the elevation once the conduit is created, but I was trying to do it when the conduit was created.&amp;nbsp;&lt;/P&gt;&lt;P&gt;I'll have to look into the options with conduit creation to see if there is an option to set elevation.&amp;nbsp;&lt;/P&gt;</description>
    <pubDate>Tue, 13 Apr 2021 12:32:21 GMT</pubDate>
    <dc:creator>djforemandesign</dc:creator>
    <dc:date>2021-04-13T12:32:21Z</dc:date>
    <item>
      <title>Conduit OD Not Modeled Correctly</title>
      <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10225144#M25347</link>
      <description>&lt;P&gt;The OD for conduit is defined in the electrical settings. I would think that these measurements are what are used when the conduit is actually modeled.&amp;nbsp;&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;But looking at the OOTB EMT the dimensions for the OD don't match what the modeled OD is.&amp;nbsp;&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;See the screenshot below for a visual of the differences:&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;&lt;span class="lia-inline-image-display-wrapper lia-image-align-inline" image-alt="OD VS ACTUAL.PNG" style="width: 740px;"&gt;&lt;img src="https://forums.autodesk.com/t5/image/serverpage/image-id/904380iABC0036A42CC1031/image-dimensions/740x379?v=v2" width="740" height="379" role="button" title="OD VS ACTUAL.PNG" alt="OD VS ACTUAL.PNG" /&gt;&lt;/span&gt;&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;For the sizes 1/2" to 2" the actual model is off by a small amount.&amp;nbsp;&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;Interesting though looking at the 3/4" conduit the OD provided by Wheatland is 0.922" which is closer to what is modeled than what is in the electrical settings.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;My question: Is there anyway that this can be accurate?&lt;/P&gt;&lt;P&gt; &lt;/P&gt;</description>
      <pubDate>Fri, 09 Apr 2021 14:16:40 GMT</pubDate>
      <guid>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10225144#M25347</guid>
      <dc:creator>djforemandesign</dc:creator>
      <dc:date>2021-04-09T14:16:40Z</dc:date>
    </item>
    <item>
      <title>Re: Conduit OD Not Modeled Correctly</title>
      <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10225158#M25348</link>
      <description>&lt;P&gt;Revit reports conduit OD in the electrical settings rounded to the 1/32".&amp;nbsp; The actual dimensions are entered to the 1/256"&lt;/P&gt;</description>
      <pubDate>Fri, 09 Apr 2021 14:20:32 GMT</pubDate>
      <guid>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10225158#M25348</guid>
      <dc:creator>timlove</dc:creator>
      <dc:date>2021-04-09T14:20:32Z</dc:date>
    </item>
    <item>
      <title>Re: Conduit OD Not Modeled Correctly</title>
      <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10225190#M25349</link>
      <description>&lt;P&gt;&lt;FONT face="comic sans ms,sans-serif"&gt;Out of curiosity. Is the actual dimension being used accessible somewhere?&amp;nbsp;&lt;/FONT&gt;&lt;/P&gt;&lt;P&gt;&lt;FONT face="comic sans ms,sans-serif"&gt;In a file or through the api?&lt;/FONT&gt;&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;&lt;FONT face="comic sans ms,sans-serif"&gt;Or is it hard coded to a certain dimension?&amp;nbsp;&lt;/FONT&gt;&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;&lt;FONT face="comic sans ms,sans-serif"&gt;Autodesk should really update the electrical settings to be able to enter dimensions to 1/256" accuracy.&amp;nbsp;&lt;/FONT&gt;&lt;/P&gt;</description>
      <pubDate>Fri, 09 Apr 2021 14:31:28 GMT</pubDate>
      <guid>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10225190#M25349</guid>
      <dc:creator>djforemandesign</dc:creator>
      <dc:date>2021-04-09T14:31:28Z</dc:date>
    </item>
    <item>
      <title>Re: Conduit OD Not Modeled Correctly</title>
      <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232766#M25350</link>
      <description>&lt;P&gt;Hello,&lt;/P&gt;
&lt;P&gt;&amp;nbsp;&lt;/P&gt;
&lt;P&gt;To have a proper control of the size, delete the existing one and recreate with the desired rounding.&lt;/P&gt;</description>
      <pubDate>Mon, 12 Apr 2021 22:56:35 GMT</pubDate>
      <guid>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232766#M25350</guid>
      <dc:creator>fabiosato</dc:creator>
      <dc:date>2021-04-12T22:56:35Z</dc:date>
    </item>
    <item>
      <title>Re: Conduit OD Not Modeled Correctly</title>
      <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232825#M25351</link>
      <description>&lt;P&gt;&lt;a href="https://forums.autodesk.com/t5/user/viewprofilepage/user-id/10674374"&gt;@djforemandesign&lt;/a&gt;&amp;nbsp;&lt;/P&gt;
&lt;P&gt;I believe this is a good question to figure out the discrepancy ...But I also believe that this difference won't result in a big problem in the coordination or the drawings. Also the tagged information will be the conduit size and not the OD. No offense to your question &lt;span class="lia-unicode-emoji" title=":slightly_smiling_face:"&gt;🙂&lt;/span&gt;&lt;/P&gt;</description>
      <pubDate>Mon, 12 Apr 2021 23:47:26 GMT</pubDate>
      <guid>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232825#M25351</guid>
      <dc:creator>Mahmoud.Ziedan</dc:creator>
      <dc:date>2021-04-12T23:47:26Z</dc:date>
    </item>
    <item>
      <title>Re: Conduit OD Not Modeled Correctly</title>
      <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232862#M25352</link>
      <description>&lt;P&gt;&lt;a href="https://forums.autodesk.com/t5/user/viewprofilepage/user-id/1220342"&gt;@fabiosato&lt;/a&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;The issue is in electrical settings the rounding doesn't allow the precision of 1/256" like the rest of Revit. It only goes to 1/32".&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;&lt;a href="https://forums.autodesk.com/t5/user/viewprofilepage/user-id/3661055"&gt;@Mahmoud.Ziedan&lt;/a&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;I understand that the difference is very minimal and it won't really affect the drawings or coordination.&lt;/P&gt;&lt;P&gt;Though depending on the number of conduit it could affect prefabrication of the racks if you are trying to avoid something through coordination, but that's probably not too common.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;The real reason I was trying to figure this out was because I'm working on creating conduit using Dynamo. Currently I'm creating the conduit based on the center line, but I would like to create it based on the top or bottom elevation as well.&lt;/P&gt;&lt;P&gt;So I was trying to figure out a way to get the actual OD of the conduit so I could plug that into a formula for the creation of the conduit.&amp;nbsp; Using the electrical settings the conduit would be created just short of the desired elevation.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;Just wanted to see if anyone knew of a way to get the OD Revit is actually using to create the conduit.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;Since the value is close I might look into possibly rounding the formula up/down to get the desired results.&lt;/P&gt;</description>
      <pubDate>Tue, 13 Apr 2021 00:15:03 GMT</pubDate>
      <guid>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232862#M25352</guid>
      <dc:creator>djforemandesign</dc:creator>
      <dc:date>2021-04-13T00:15:03Z</dc:date>
    </item>
    <item>
      <title>Re: Conduit OD Not Modeled Correctly</title>
      <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232877#M25353</link>
      <description>&lt;P&gt;&lt;a href="https://forums.autodesk.com/t5/user/viewprofilepage/user-id/10674374"&gt;@djforemandesign&lt;/a&gt;&amp;nbsp;&lt;/P&gt;
&lt;P&gt;Okay I got your point, yes I think rounding will solve this issue otherwise you shall use the physical dimension of the conduit in dynamo and not relying on the OD parameter and I think this gonna be very complicated so the best solution is rounding.&lt;/P&gt;</description>
      <pubDate>Tue, 13 Apr 2021 00:24:47 GMT</pubDate>
      <guid>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232877#M25353</guid>
      <dc:creator>Mahmoud.Ziedan</dc:creator>
      <dc:date>2021-04-13T00:24:47Z</dc:date>
    </item>
    <item>
      <title>Re: Conduit OD Not Modeled Correctly</title>
      <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232891#M25354</link>
      <description>&lt;P&gt;&lt;a href="https://forums.autodesk.com/t5/user/viewprofilepage/user-id/3661055"&gt;@Mahmoud.Ziedan&lt;/a&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;Yeah I have it working for the center line, but realized that the bottom elevation is not an even height so wanted to try to figure out how to get the bottom/top at the elevation I want instead of the center.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;The only problem is the way I'm going about it right now is I'm creating lines in Dynamo to represent the conduit then once I have all the lines created I use them to create the conduit. So the line has to be at the correct elevation and I won't have the physical conduit until after the lines are made.&lt;/P&gt;&lt;P&gt;I know that after the conduit is made I could use Dynamo to change the elevation of the conduit, but that is just going back through what I already did.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;Maybe that's what I'll have to do if the rounding doesn't work.&amp;nbsp; I'll figure it out....eventually. Just was hoping for an easy solution.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;I appreciate your help though. Wish Autodesk didn't force the rounding in the electrical settings for some reason.&lt;/P&gt;</description>
      <pubDate>Tue, 13 Apr 2021 00:32:44 GMT</pubDate>
      <guid>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232891#M25354</guid>
      <dc:creator>djforemandesign</dc:creator>
      <dc:date>2021-04-13T00:32:44Z</dc:date>
    </item>
    <item>
      <title>Re: Conduit OD Not Modeled Correctly</title>
      <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232969#M25355</link>
      <description>&lt;P&gt;The conduit setting only report rounded to the 1/32".&amp;nbsp; You can still enter in to at least the 1/256", maybe even to the 1/512" I'm not certain if it goes more accurate or not.&amp;nbsp; The conduit is modeled in to at least the 1/256" accuracy.&amp;nbsp;&amp;nbsp;&lt;BR /&gt;as for the issue of dynamo, I am not sure if you can set the vertical justification of the conduit using it or if you would have to set that first in your conduit placement tools.&amp;nbsp; Once you start the conduit tool the ribbon has the justification button that you can use to set the vertical and horizontal justifications.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;I know with Revit 2019 Dynamo you can get the bottom elevation of conduit, and change the values once it is placed.&lt;/P&gt;</description>
      <pubDate>Tue, 13 Apr 2021 01:17:16 GMT</pubDate>
      <guid>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10232969#M25355</guid>
      <dc:creator>timlove</dc:creator>
      <dc:date>2021-04-13T01:17:16Z</dc:date>
    </item>
    <item>
      <title>Re: Conduit OD Not Modeled Correctly</title>
      <link>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10234214#M25356</link>
      <description>&lt;P&gt;So OOTB at least for Revit 2020 (I assume for all years) the electrical settings for a 3/4" EMT is the OD is set to 15/16".&lt;/P&gt;&lt;P&gt;When modeled this is actually modeled at 59/64". This is closer to the actual size of the conduit.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;If you go in and edit this OD to something else no surprise Revit rounds to 1/32", but when you actually model the conduit the OD matches what it rounds to.&amp;nbsp;&lt;/P&gt;&lt;P&gt;So you can't get the conduit OD back to 59/64" once you edit the OOTB settings.&amp;nbsp;&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;Again not sure why Autodesk is rounding these settings when the rest of Revit is 1/256" accuracy.&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;&amp;nbsp;&lt;/P&gt;&lt;P&gt;For the conduit creation you can edit the elevation once the conduit is created, but I was trying to do it when the conduit was created.&amp;nbsp;&lt;/P&gt;&lt;P&gt;I'll have to look into the options with conduit creation to see if there is an option to set elevation.&amp;nbsp;&lt;/P&gt;</description>
      <pubDate>Tue, 13 Apr 2021 12:32:21 GMT</pubDate>
      <guid>https://forums.autodesk.com/t5/revit-mep-forum/conduit-od-not-modeled-correctly/m-p/10234214#M25356</guid>
      <dc:creator>djforemandesign</dc:creator>
      <dc:date>2021-04-13T12:32:21Z</dc:date>
    </item>