When trying to replicate the flow through a section of HEPA filter, since I don't know the permiability constant I am using the Head Capacity Curve function. I have pressure drop (in H20) versus Air Velocity (ft/min) and have converted the velocity to flow rate based on the area of the filter section my flow volume is through.

 

However, the pressure drop that results is approximately double what was input in the Head Capacity Curve. Any ideas as to why this happens?

 

Thanks

Product Support
662 Posts
232 Kudos
Registered: ‎08-24-2011

Re: Modeling HEPA Filters in CFDesign using Head Capacity Curve

02-07-2012 09:54 AM in reply to: TitusCFD

What values did you put into the hea capactiy curve (HCC)?  Screenshot might help here.

Did you try adding more mesh?

2D Resistances parts can also provide more accurate results at times.

 

Are you testing the setup in a smaller model that isn't NDA that you are willing to share?

 

Thanks,

Royce



Royce Abel
Active Member
8 Posts
0 Kudos
Registered: ‎02-07-2012

Re: Modeling HEPA Filters in CFDesign using Head Capacity Curve

02-07-2012 10:03 AM in reply to: Royce_adsk

I have attached the setup I used, and the values I loaded for the HCC. I haven't tried to add more mesh yet.

 

One weird thing did occur, when I initally solved the results were approximately 0.17in H20, and some of the variables in the convergence plot had not seemed to quite level off. When I ran additonal interations the pressure drop jumped from 0.17 in H20 to 0.59 in H20.

Product Support
662 Posts
232 Kudos
Registered: ‎08-24-2011

Re: Modeling HEPA Filters in CFDesign using Head Capacity Curve

02-07-2012 10:06 AM in reply to: TitusCFD

The *.cfdst file isn't a very useful file to upload, create a support share file (file menu_save share file) and upload that instead.

 

See this table for more information on CFD file types: 

http://www.cfdesign.com/OnlineHelp/2011/User%20Interface/File/Working%20with%20Files.htm

 

Thanks!

Royce



Royce Abel
Active Member
8 Posts
0 Kudos
Registered: ‎02-07-2012

Re: Modeling HEPA Filters in CFDesign using Head Capacity Curve

02-07-2012 11:10 AM in reply to: Royce_adsk

See attached for support share file.

 

I refined the mesh and re ran, and it had very similar results as mentioned previously.

Product Support
662 Posts
232 Kudos
Registered: ‎08-24-2011

Re: Modeling HEPA Filters in CFDesign using Head Capacity Curve

02-07-2012 01:20 PM in reply to: TitusCFD

The poor performance is associated with a character used in the material name that is not supported.  Try changing the name of the resistance to "2 inch HEPA Filter Resistance".  After I removed the " character the pressure drop was more inline with expectations.

 

I already tested future builds and warnings are given when this character is used.

 

-Royce



Royce Abel
Active Member
8 Posts
0 Kudos
Registered: ‎02-07-2012

Re: Modeling HEPA Filters in CFDesign using Head Capacity Curve

02-07-2012 01:57 PM in reply to: Royce_adsk

Thank you solved my issue.

 

Can you expect a similar issue when using any punctuation? for just the "?

Product Support
662 Posts
232 Kudos
Registered: ‎08-24-2011

Re: Modeling HEPA Filters in CFDesign using Head Capacity Curve

02-07-2012 02:56 PM in reply to: TitusCFD

Here is a warning screen with the list of characters to stay away from.

 

-Royce

 

2-7-2012 5-55-33 PM.png



Royce Abel
Active Contributor
33 Posts
0 Kudos
Registered: ‎11-02-2011

Re: Modeling HEPA Filters in CFDesign using Head Capacity Curve

03-23-2012 12:27 PM in reply to: TitusCFD

Is there a standard Head Capacity Curve for HEPA filters?  Where can that information be found?