Discussion Groups
Robot Structural Analysis
Distinguished Contributor
4 Kudos
Vertical Panels
497 Views, 13 Replies
01-13-2013 10:58 PM
Dear Colleagues
I faced a probem in the shear walls which I have chosen from the middle core of the building . As you see in the capture (1&2) , when I use “ analytical method “ sometimes a message appears saying that  there is (unknow error for the panel) and the reinforcement appears to be not logical as appear in the capture (1) .
This case meet  me in many vertical panels(walls) in the attached model.
Could you help me to overcome this problem ?
http://www.2shared.com/file/5yTRJtF4/Vertical_Panels.html
Note : If you send  a captures for explanation , Kindly send it as attached.
Thanks  in advance
Refaat
Product Support
760 Kudos
Re: Vertical Panels
01-14-2013 04:20 AM in reply to: refaat
As far as I can see the area of reinforcement cannot be calculated in one node of the panel. I think that you can use the results from the neighboring elements instead. The values of Ax(-) and Ax(+) are 0s therefore the map will not be displayed. In case you have the problem with other maps make sure the range of the scale is defined correctly.
Artur Kosakowski
4 Kudos
Re: Vertical Panels
01-15-2013 01:20 AM in reply to: Artur.Kosakowski
Dear Artur
- Thanks , but I would like to know , what are the main causes for such type of messages "unknown error for the panel ".
-   And how I can avoid in  other  models?
 That is because I will not be able to submit my calculation report with such errors.
With Regards
Refaat
Product Support
760 Kudos
Re: Vertical Panels
01-15-2013 04:26 AM in reply to: refaat
The reinforcement calculations is based on the iterative process. In the situations when for some reason this iterative process fails to converge this message is displayed.
If this happens you may try to change meshing of the panel. If this fails all you can do is to report such situation and we have to investigate what actually caused the reinforcement calculation process to fail.
I think this should be possible. Having the results in all but one verification points (all centers of surface elements and all nodes but one) it is possible to estimate the value in the missing node from the neighboring results. As far as I can see it is also possible to display maps providing one enters the reasonable values of max and min values on the scale.
Artur Kosakowski
4 Kudos
Re: Vertical Panels
01-17-2013 01:12 AM in reply to: Artur.Kosakowski
Dear Artur
After I investigated the case by changing  the mesh (size -type)  , I have noted that only in  one situation the message ( Unknown error for panel ) is disappeared when I calculated the required reinforcement without included (ACC) cases.
Also, I have noted that when I included  (ACC) but calculating the panel using one of the simplified method instead of analytical method, also the message is disappeared, but of course we can't use it in shear walls.
Based on above I can say that there is something to calculate the membrane forces during the seismic cases because even when I changed the used code (IBC2000&IBC2006&IBC2009 and UBC97) it gave the same scenario.
Note : Kindly take a look to the attached captures.
What can I do? , I am really worried from this problem .
Thanks for any assistance
Refaat
Product Support
760 Kudos
Re: Vertical Panels
01-17-2013 01:57 AM in reply to: refaat
As I wrote previously check the values in nodes and centers of these elements in the reinforcement table. Most likely only one of them is missing which influences the display of maps but this should allow you for the estimation of reinforcement areas in these locations. As far as I can tell this situation happens in regions that require low reinforcement. In addition you can try to select these elements and refine mesh in these locations.
You can also try to use the Wood and Armer method.
Please mind that you should not use the globally averaged forces for panels with join with other panels that are not in the same plane (wall and slab).
Artur Kosakowski
4 Kudos
Re: Vertical Panels
01-17-2013 02:25 AM in reply to: Artur.Kosakowski
Dear Artur
Thanks for your fast response .
-Do you mean (Wood and Armer method) , Can be used for shear walls. As far as I know that it is not considered the membrane forces in shell element ? Pleases , confirm.
- Is it correct ?" I used (globally averaged forces)  for two panels(walls) (both vertical) but the angle between them (90 Degree )".
- Kindly , could you send me the capture in your previous post as attached ? because I couldn't open it.
Thank you very much
Refaat
Product Support
760 Kudos
Re: Vertical Panels
01-17-2013 03:14 AM in reply to: refaat
refaat wrote:
Dear Artur
It does not include Nxx (so indeed if these forces are large than it is better to use the analitical one) but includes Nxx and Nyy.
If you have any not vertical panel at the top or bottom edge of the wall (panel) then you should not use this option.
Attached.
Artur Kosakowski
4 Kudos
Re: Vertical Panels
01-17-2013 07:02 AM in reply to: Artur.Kosakowski
Dear Artur
Please , take a look to  the attached capture which shows high values(Nxx& Nyy ) at the nodes where ROBOT can't calculate the required reinforcement compared with the other elements.
What is your comment about these results ?
Note : if you use any capture for explanation . Kindly , send it as attached.
Thanks for your cooperation
Refaat
Product Support
760 Kudos
Re: Vertical Panels
01-18-2013 03:19 AM in reply to: refaat
I think that the results in tee corners are influenced by the fact that this is very 'rigid' part due to sizes of the beams. Actually it seems that you may say that in reality there is no wall in these locations but beams instead.
Artur Kosakowski