According to the results I am not expecting to be seeing the "Unsatisfactory Load Capacity of the Column" message. Any reason why it could still be appearing?

Please use plain text.
Product Support
Artur.Kosakowski
Posts: 5,115
Registered: ‎12-17-2010

Re: Unsatisfactory Load Capacity of the Column

10-04-2012 04:51 AM in reply to: stroxy

Could you attach the file with this column please?



Artur Kosakowski
Please use plain text.
Product Support
Artur.Kosakowski
Posts: 5,115
Registered: ‎12-17-2010

Re: Unsatisfactory Load Capacity of the Column

10-05-2012 01:09 AM in reply to: Artur.Kosakowski

Large bi-directional shear for seismic combinations.

 

shear1.PNG

 

If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.



Artur Kosakowski
Please use plain text.
Mentor
stroxy
Posts: 191
Registered: ‎12-06-2011

Re: Unsatisfactory Load Capacity of the Column

10-05-2012 03:40 AM in reply to: Artur.Kosakowski

Error message still remains after manual modification of rebar to correct safety factor. See my earlier attachment.  

  

Please use plain text.
Product Support
Artur.Kosakowski
Posts: 5,115
Registered: ‎12-17-2010

Re: Unsatisfactory Load Capacity of the Column

10-05-2012 03:47 AM in reply to: stroxy

I'm not sure if I understand you correctly. What have you modified: spcaing of the stirrups? The best seems to be the increase of a cross section of the column itself.



Artur Kosakowski
Please use plain text.
Mentor
stroxy
Posts: 191
Registered: ‎12-06-2011

Re: Unsatisfactory Load Capacity of the Column

10-05-2012 04:27 AM in reply to: Artur.Kosakowski

Increased stirrup diameter in some cases and yes reduced stirrup spacing in others.  Your suggestion on increasing column dimension is however well noted ... but unfortunately  sometimes Architectural constraints determine how much column dimensions can be increased (the ever continuing saga between engineers and architects :manlol:)

 

Also, Sometimes when one increases column dimensions, then huge plastic moments capacity develops in the column thus making it more difficult to satisfy capacity design requirement in shear.

 

In  any case, I should expect the  error message to disappear once the safety ratios for the governing case is greater than 1 ... correct?

Please use plain text.
Product Support
Artur.Kosakowski
Posts: 5,115
Registered: ‎12-17-2010

Re: Unsatisfactory Load Capacity of the Column

10-05-2012 06:56 AM in reply to: stroxy

Yes, the error should no longer be displayed  when all (for each of defined seismic combinations) safety ratios for shear are above 1.



Artur Kosakowski