Discussion Groups

Robot Structural Analysis

Reply
New Member
eunjucha
Posts: 1
Registered: ‎11-21-2011

Thermal Load

611 Views, 1 Replies
11-21-2011 05:51 PM

Hi,

 

I would like to know the formula of thermal load for steel you have on load definition based on BS5950 and BS8110.

i try to put the temperature difference of dT 10C in TZ direction and run annalysis.

i expect the emperature induced loads accounted for 10% to 20% of the total axial load though, it does account less than 1 to 2 % of the total axial load in the results.

 

i have the formula of it , Pt, which is following

Pt = 1.2xk x A x E x (12x10-6) x TD

1.2 = load factor

k = Thermal expansion factor = 0.8

A = Gross area of section of steel

E =Modulus of Elasticity of steel =  205 kN/mm2

TD = temp difference (C)

 

please help me up to solve that problem.

 

thanks and regards,

EunJu

Please use plain text.
Product Support
Artur.Kosakowski
Posts: 5,115
Registered: ‎12-17-2010

Re: Thermal Load

11-21-2011 11:48 PM in reply to: eunjucha

You should define TX instead. TZ (or TY) being the difference of temperature between top and bottom (left and right) fibers cause bending rather than tension/compression. See http://docs.autodesk.com/RSA/2012/ENU/filesROBOT/GUID-E4AB6038-D264-45C9-80F9-B06BC687794-448.htm

 

If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.



Artur Kosakowski
Please use plain text.