Robot Structural Analysis Forum
Welcome to Autodesk’s Robot Structural Analysis Forums. Share your knowledge, ask questions, and explore popular Robot Structural Analysis topics.
STEEL DESIGN - EC3 - Failing Members
6 REPLIES 6
Burgon87
1410 Views, 6 Replies
Please can someone help?
I have two members that are loaded similarly and one fails and the other does not, can someone tell me within the results attached why one is failing?
Many Thanks.
STEEL DESIGN
CODE:
   BS-EN 1993-1:2005/NA:2008/AC:2009,  Eurocode 3: Design of steel structures.
ANALYSIS TYPE:
   Member Verification
CODE GROUP:
MEMBER:
   63  Beam_63POINT:   1COORDINATE:   x = 0.75 L = 5.715 m
LOADS:
Governing Load Case:
   17 1.2DL + 1.2LL + 1.2WL(S)  (1+2+3+4+5+14)*1
MATERIAL:
S355  ( S355 )       fy = 355 MPa
   SECTION PARAMETERS:  CHS 114.3x5
h=114.300 mm gM0=1 gM1=1
b=114.300 mm Ay=1094.986 mm2 Az=1094.986 mm2 Ax=1720.000 mm2
tw=5.000 mm Iy=2570000.000 mm4 Iz=2570000.000 mm4 Ix=5140000.000 mm4
tf=5.000 mm Wply=59774.117 mm3 Wplz=59774.117 mm3
INTERNAL FORCES AND CAPACITIES:
N,Ed = -334.30 kN  My,Ed = 12 kN*m Mz,Ed = -2 kN*m Vy,Ed = -1.31 kN
Nt,Rd = 610.60 kN My,pl,Rd = 21 kN*m Mz,pl,Rd = 21 kN*m Vy,T,Rd = 136.02 kN
My,c,Rd = 21 kN*m Mz,c,Rd = 21 kN*m Vz,Ed = -5.76 kN
My,N,Rd = 14 kN*m Mz,N,Rd = 14 kN*m Vz,T,Rd = 136.02 kN
Tt,Ed = 7 kN*m
Class of section = 1
     LATERAL BUCKLING PARAMETERS:
      About Y axis:       About Z axis:
VERIFICATION FORMULAS:
Section strength check:
N,Ed/Nt,Rd = 1 < 1   (6.2.3.(1))
(My,Ed/My,N,Rd)^ 2 + (Mz,Ed/Mz,N,Rd)^2 = 1 < 1   (6.2.9.1.(6))
Vy,Ed/Vy,T,Rd = 0 < 1   (6.2.6-7)
Vz,Ed/Vz,T,Rd = 0 < 1   (6.2.6-7)
Tau,ty,Ed/(fy/(sqrt(3)*gM0)) = 0 < 1   (6.2.6)
Tau,tz,Ed/(fy/(sqrt(3)*gM0)) = 0 < 1   (6.2.6)
Section OK !!!
STEEL DESIGN
CODE:
ANALYSIS TYPE:
   Member Verification
CODE GROUP:
MEMBER:
   64  Beam_64POINT:   1COORDINATE:   x = 0.75 L = 5.715 m
LOADS:
MATERIAL:
N,Ed = 308.06 kN  My,Ed = 17 kN*m Mz,Ed = -0 kN*m Vy,Ed = -0.25 kN
Nc,Rd = 610.60 kN My,pl,Rd = 21 kN*m Mz,pl,Rd = 21 kN*m Vy,T,Rd = 120.07 kN
Nb,Rd = 610.60 kN My,c,Rd = 21 kN*m Mz,c,Rd = 21 kN*m Vz,Ed = -8.49 kN
My,N,Rd = 15 kN*m Mz,N,Rd = 15 kN*m Vz,T,Rd = 120.07 kN
Tt,Ed = 9 kN*m
N,Ed/Nc,Rd = 1 < 1   (6.2.4.(1))
(My,Ed/My,N,Rd)^ 2 + (Mz,Ed/Mz,N,Rd)^2 = 1 > 1   (6.2.9.1.(6))
Incorrect section !!!
6 REPLIES 6
tony.ridley
in reply to: Burgon87
one is in tension, one is in compression?
Artur.Kosakowski
Please increase the precision of displaying the results. From the info you provided I assume it is sort of 0.999 < 1 for one of the bars and 1.001> 1 for the other.
Artur Kosakowski
jo2ny
in reply to: Artur.Kosakowski
I have a question regarding a verification note.
Is it possible to have this: Tau,ty,Ed/(fy/(sqrt(3)*gM0)) = 1.41 > 1.00 (6.2.6)
All the efforts in the bar are very small.
Artur.Kosakowski
in reply to: jo2ny
Torsion.
Artur Kosakowski
ouoba.diassiboalain
in reply to: jo2ny
What is  the meaning of Tau,ty,Ed  and what is the formula to calculate it ?
Thanks!
Hi @ouoba.diassiboalain
Follow the recommendations of EN 1993-1-1 Chapter 6.2.6
Best regards
