Hey guys i want to make a connection like in the attached file as a column beam connection. However i can't find the right type in the steel design connections. Also i want it to be subjected to a shear of 270 kN and nothing else. How is it possible?
Solved by Artur.Kosakowski. Go to Solution.
Option3: Replace the tube with an I section on a short part of the column where the beam is located. This should allow you to design the shear plate, its welds as well as the bolts.
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Sorry i didn't specify my question. I need to design a fin plate on a column made of HEB 300 and Beam of HEM 300 subjected to 270 kN shear. ( see atached file)
+1 for Artur, this is the way i also use in such cases, but be carefull because actually the shear force acting at the beam's end causes a moment at the centerline of the column (if the connection is modeled as pinned) because of the deistance of the c.m of the column's section and the point that the shear is transfered... This of course also happens in case of not using circular or tubular columns.
HI @belrefai
This type of connection is not supported.
Refer to Steel connection types in Robot