Robot Structural Analysis

Reply
Contributor
JIHADTM
Posts: 14
Registered: ‎11-14-2011
Accepted Solution

slab punching

307 Views, 1 Replies
10-16-2012 12:28 AM

Hello,

I'm checking the slab punshing by using robot 2013 using ACI sode,  I defined from the design tab menu  reinforcement wall/slab options code parameter) the properties of the rc slab (see attachement) as follow:

Concrete cover = 30mm.

However when I calculated the punching by software, I found out that the cover has been taken equal to 50mm ????.

please clarrify how I can control determination of concrete cover used by software. See attachement.

Please use plain text.
Product Support
Artur.Kosakowski
Posts: 5,115
Registered: ‎12-17-2010

Re: slab punching

10-16-2012 12:50 AM in reply to: JIHADTM

Check what reinforcement label you actually assigned to panel 21. Looking at the picture you attached I got the feeling that you compared reinforcement label that was assigned to this panel (provided reinforcement) with the one that wasn't (required reinforcement).

 

If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.



Artur Kosakowski
Please use plain text.