Seismic Vs Spectral
16 REPLIES 16
Message 1 of 17
tony.ridley
2545 Views, 16 Replies
Seismic Vs Spectral
Rafal/Artur,
It seems to me the difference between seismic and spectral analysis in Robot is that;
In SEISMIC analysis;
  • Based on the chosen code, seismic analysis works out the response spectrum etc automatically based on the input parameters (region etc).
  • The user can set an expected base shear that Robot will limit seismic base shear to.
  • Eccentricity option is available within the seismic options (can leave eccentricity zero in the preceeding modal case)
But using SPECTRAL method;
  • I need to define the correct response spectrum;
  • I need to apply any eccentricity in the preceeding modal analysis;
  • I need to do an initial run, then go back and do a second iteration to apply scaling factors to limit my base shear to the expected value.
Please confirm if my assumptions are correct, feel free to make corrections!
Tony
Tags (2)
16 REPLIES 16
Message 2 of 17
@tony.ridley wrote:
Rafal/Artur,
Correct.
For selected codes it is possible. For the ones this option is not available you can 'scale' it defining a load combination with the appropriate load factor.
Is available in both modal analysis (accurate solution) and seismic case (simplified approach). It is the either / or choice.
Correct
Correct
Correct
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Artur Kosakowski
Message 3 of 17
MARIOS75
in reply to: Artur.Kosakowski
i' ve noticed that in spectral analysis the results are influenced by the the damping ratio (controled in the modal analysis menu).
How is this possible?
Message 4 of 17
Artur.Kosakowski
in reply to: MARIOS75
Intended for situation when you have two spectra with e.g. 1% and 5 % damping and you want to average them. Then what you type in the modal analysis e.g. 3% influences the way these spectra are averaged.
Artur Kosakowski
Message 5 of 17
MARIOS75
Thank you Artur,
 5% damping will have no influence on the spectrum, is that right?
Message 6 of 17
Artur.Kosakowski
According to my knowledge if you do not average spectra the value of damping should be irrelevant.
Artur Kosakowski
Message 7 of 17
MARIOS75
i have no averaged spectrum, just a single custom spectrum defined from a text file.
Damping (the one controled by the modal analysis menu) seems  to influence the results in an inverse maner, high damping values give high response values.
This behaviour is more clear in systems with many degrees of freedom.
Message 8 of 17
Artur.Kosakowski
In such case I need to have a closer look at this situation. Could you send me the rtd file and indicate the differences in results you noticed as well as the corresponding values of damping you set in the parameters of the modal case please?
Artur Kosakowski
Message 9 of 17
MARIOS75
Here it is.
You can try some values of damping (e.g 1%, 50%) in the modal analysis menu and check the the columns Fx reaction.
Message 10 of 17
Artur.Kosakowski
As far as I can see the results for single modes and SRSS combinations are the same. The difference is for CQC combinations but this is justified as damping is included in the formula.
http://docs.autodesk.com/RSA/2012/ENU/filesROBOT/GUID-9A9795B9-E2B1-4F70-BC47-FF61A312699-621.htm
Artur Kosakowski
Message 11 of 17
MARIOS75
You are right about the CQC rule, i missed the fact that it's damping dependant.
Thank you.
Message 12 of 17
can you please explain ( maybe in a simple example) the last question
I am new to spectral analysis, and I dont understand in the second interation how can I apply the  scaling factors and how to get this factors?
Thank you
Message 13 of 17
Artur.Kosakowski
You can check the sum of reactions and compare it to the targeted value. This will give you the required scaling factor. Then you can e.g. use the corresponding load factor for given seismic spectral case.
Artur Kosakowski
Message 14 of 17
That is, check the sum of reactions for the dominant mode in each direction. (not the CQC combo)...
Tony
Message 15 of 17
I have a question over the scaling factor for the modal masses that are added in a modal / spectrum analysys ,
With a given spectrum (acceleration spectrum)
Costa Rica Code stablishi  a Seismic Base Shear by
V= W x C,
where C= FED x R, W the seismic mases
Since the Dunamic spectral factor  "FED" comes from the spectrum is correct to suposse that
the scaling factor for modal masses in the RSA Analysys tool is is R?
Best Regards ,
Rodolfo R
Message 16 of 17
Hola Rodolfo, dijiste que  sos de Costa Rica? Sera que nos podemos poner en contacto para hacerte algunas preguntas de Robot, mi numero es el 8742179.
Message 17 of 17
Hola mucho Gusto Rodolfo Rodriguez ,
Si tiene alguna consulta , con mucho gusto puede contactarme al correo
rrodriguez@ijlcr.com
