Message 1 of 9
85778RSAPRO_2012_0F
551 Views, 8 Replies
RC Wall
Hi
Why can I not calculate required reinforcement for RC walls. I got the attached message.
Can you help me with this.
Waleed Khalid
8 REPLIES 8
Message 2 of 9
You have to set the code as
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Artur Kosakowski
Message 3 of 9
I got another message. Why openings are not taken into account? What that's mean for reniforcemnt?
See attached screenshot
Waleed Khalid
Message 4 of 9
The opening is too large for the used calculation method (its presence cannot be ignored). You can set the object type of this panel as the floor (see the attached picture) and then calculate required reinforcement and provided one in the RC Slab Reinforcement module instead.
Artur Kosakowski
Message 5 of 9
in reply to: Artur.Kosakowski
Artur,
I am getting a similar problem with BS EN1992-1-1:2004 - is there a British equivalent I can switch to? and will that change all of the analysis I've done to date on the structure to these codes?
Thanks!
Nigel
Message 6 of 9
Artur.Kosakowski
No, the only supported code for RC Walls is French NAD for EC2. In case it is acceptable solution you can deign the wall according to the BS EN in the RC Slab Required module instead.
The change of the code will not influence the already designed elements. You may also make a copy of the rtd file and use each of them for design according to a selected code (BS EN vs. NF EN).
Artur Kosakowski
Message 7 of 9
Hi Artur,
Do you know what difference it will have if I design as RC wall using slab method to BS EN?
Message 8 of 9
Also, I have just switched the structure object to be a panel not a wall - is this what you mean? And leave the reinforcement type as RC wall?
Message 9 of 9
Artur.Kosakowski
Correct.
The reinforcement type depends on the internal forces you want to include in the design and the reinforcement direction you decide on.
Artur Kosakowski