Hello
How I can model rc plate on steel beam. If I model it simple way (just adding beams under teh edge of plate), I don't get correct bending moments in beam.
Ragnar
Solved by Artur.Kosakowski. Go to Solution.
What do you mean by "I don't get correct bending moments"?
Model please.
I added very simple test file where are 3 situations (plate and steel beams, plate and steel beams with offset, and steel beams with cladding). I expect that result should be like using cladding but if there is a plate the bending moment in steel beam ise much smaller than using just a cladding.
They are not the same for two reasons:
1. Part of the bending is transferred by the slab
2. For the slab model the 'stiffness' of the beams is "smaller" than for the cladding model as they are defined at the same level as the panel. For the offset solution you get axial force (tension) instead of bending.
You may try:
1. Use the orthotropic definition of the slab's thickness with the reduced stiffness coefficient in the direction of the beams
2. Replace HEA200 sections with a user defined one which have increased IY value
What about calculation of required reinforcement for orthotopic plate? Should I change something?
Can I use the same solution if there are concrete beams?
Reinforcement will be calculated for the internal forces obtained during static analysis of a model with the orhothropic slab defined assuming the indicated thickness of the slab.
The question is what kind of connection between the beams and the slab you actually have and if you 'can' assume that the slab works in one direction only.
IMHO for 'offsets' yes but I'd rather assume that the slab works in both directions.
If I have a beams in both direction (plate works in two-way) then I can't use plate orthotrophy. And if I want to calculate beams also then the increased Iy is not an option also. Any tips?
In such case there is no need to do so.
Steel or concrete beams?
If it is not troublesome I'm happy to hear both version (steel beams and concrete beams under the plate).
For RC:
http://forums.autodesk.com/t5/Robot-Structural-Ana
For steel: do you intend to design your deck as a composite (steel beam working together with a concrete slab) or a deck is only a load for steel beams?
Plate is only a load on steel beams. Claddings ar not a good options beacuse if the plate is continous then the support reactions are different.
1. Define beams with the increaxded value of Iy
2. Calculate a model
3. Create a group for each beam sepatrately or for selection of beams for which you want to use the same section
4. Assign the sections you want to perform the design for to each of the groups
5. Run group verification or design